im a GSR engineer but not from a plumbing background.
I have a customer with an open vented system that is having to bleed radiators downstairs and upstairs every few weeks.
I asked a plumber about this and he said it was either
1. A leak allowing air into system
2. The expansion pipe rises above the F&E tank by only 300mm and that this would allow air into the system.(there is almost no extra room to extend the expansion pipe above the tank due to limited space)
The solutions are to obviously find and stop the leak if there is one.
Or he also advised (and this were I have serious doubts!) to put a stop end on the expansion pipe and any expansion in the system will travel back up the return pipe into the F&E tank.
If after a few weeks the problem reoccurs then I obviously have a leak and could take the stop end off the expansion pipe.
This is my first time posting here so only helpful advice please,be gentle!
 
Difficult to say exactly without inspection.
Could be a small leak somewhere esp if ground floor suspended, does expansion tank seem to be filling regularly?
Could be build up of sludge in system creating Hydrogen in the rads, check for cold spots usually bottom of rad cooler than the top.
Take a peak inside the expansion tank, if its really dirty with sludge that could be the problem.
As Gasmk1 said do not cap off the expnsion pipe
 
Thanks I new that didn't sound right but this guy that advised has been a plumber/heating engineer for 20 years...makes you wonder!!
 
Thanks I new that didn't sound right but this guy that advised has been a plumber/heating engineer for 20 years...makes you wonder!!

It never ceases to amaze me !
As above, don't stop end the vent.
It could be pulling air in the vent. A lot depends on the position of the pump in relation to other things.
You could send photos of pump, tanks, etc
 
Status
Not open for further replies.

Reply to Open vented system,advised to cap off expansion pipe?? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

    • Like
Hi I recently did some pipe insulating in my loft. The only two I didn't do were the vent pipes. Not sure if that is the right term for them? They are the pipes that feed water back into the top of the tanks when there is excess, presumably from steam, expansion, etc. The one going to the cold...
Replies
2
Views
331
Hi, I'm new to the forum and just some background on myself. I have 4 years experience as a plumber but haven't worked in the trade in 15 years. I would say my overall knowledge is not great as I did most of the 4 years working on rinse and repeat estates of houses. I was also quite young and...
Replies
13
Views
569
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem could be. We have a biomass boiler and stratification tank set up and recently had an issue with boiler pressure dropping off when the system was cold...
Replies
9
Views
344
Hello, I have just installed a vented McDonald 250L thermal store, it is for multi fuel but currently just connected to a standard oil boiler in the garage which is fully pumped to the TS, the system has two pumps both basic 3speed Grunfoss, one on the boiler return and the other on the CH flow...
Replies
22
Views
1K
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and plasterboard celling. I have got unvented pressurized RM Cylinders hot water system with 27KW Worchester gas boiler with expansion vessels . When...
Replies
2
Views
449
losing pressure
L
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock