Hi
I am having my kitchen revamped and have removed the sink and waste pipes.

However the condensate drain pipe was connected to the waste pipe so I therfore temporarily dropped the condensate drain into a bucket.

I have since turned on the boiler so my wife could take a shower and noticed water vapour/steam coming from the condensate drain pipe...

Is this normal or a problem with the boiler which is an Isar Ideal HE24.

Many thanks in advance for any repies.

Mr Fog
 
Don't run the boiler into a bucket with the isar series the condense isn't trapped so needs a trap inline, normally just below the boiler / under the kitchen worktop

It's basically what's going out the flue in the condense pipe so it's products of combustion

Best option is enlist the services of a gas safe engy to put the condense right and maybe service the boiler
 
Yes, it's a problem. If this "vapour/steam" is being emitted into your house so, probably, is flue gas. Turn off the boiler and get a Gas Safe engineer to come and sort it out for you.

Broadly speaking, a condensate drain needs to be treated with as much respect as the flue. Don't mess with it or you may end up with a dead family.
 
Last edited:
Don't run the boiler into a bucket with the isar series the condense isn't trapped so needs a trap inline, normally just below the boiler / under the kitchen worktop

It's basically what's going out the flue in the condense pipe so it's products of combustion

Best option is enlist the services of a gas safe engy to put the condense right and maybe service the boiler

So are you saying the Isar does not have an S Trap fitted?
 
Last edited:
I believe that model does have an internal S-trap:

http://idealboilers.com/installer/wp-content/uploads/sites/2/2013/08/204256-2-7.pdf

but the OP's description strongly suggests either it is not performing its function correctly or there is a HX leak.

If there's an internal trap why is an external to the boiler trap required

It's prob just in case the condense line gets blocked, like on the solos

IMG_2897.PNG
 
If there's an internal trap why is an external to the boiler trap required
It's prob just in case the condense line gets blocked, like on the solos

You seem to have found another version of the ISAR HE 24 than I did. The manual I cited is dated Aug 2009 and does not show an external trap. Anyway, the symptoms certainly suggest no trap (likely) or an empty trap (less likely) and either way I hope we can agree that the OP should stop using the boiler until the condensate drain has been reviewed and reconnected properly by a GSR.

[I've edited my original comment appropriately.]
 
Last edited:
You seem to have found another version of the ISAR HE 24 than I did. The manual I cited is dated Aug 2009 and does not show an external trap. Anyway, the symptoms certainly suggest no trap (likely) or an empty trap (less likely) and either way I hope we can agree that the OP should stop using the boiler until the condensate drain has been reviewed and reconnected properly by a GSR.

[I've edited my original comment appropriately.]

2008 mine so one year apart

And tbh think there's no trap

As on hot water the trap should of filled / stopped steaming / venting poc to the room within 10-15 mins
 
Thats a bit of a no no Mr Fog products of combustion with be escaping into your kitchen get it reconnected temporarily until your revamp
 
2008 mine so one year apart

And tbh think there's no trap

As on hot water the trap should of filled / stopped steaming / venting poc to the room within 10-15 mins
Before mounting the boiler on the wall, the condensate drain (provided in the h/ware pack) must be connected from the boiler ‘S’ trap to a drainage point, preferably within the building.

Ensure that the condensate trap is full of water before commissioning the boiler . Refer to Frame 26.

from the instructions it hought all isars had this difficult to remove and prone to blocking s trap fitted
 
Before mounting the boiler on the wall, the condensate drain (provided in the h/ware pack) must be connected from the boiler ‘S’ trap to a drainage point, preferably within the building.

Ensure that the condensate trap is full of water before commissioning the boiler . Refer to Frame 26.

from the instructions it hought all isars had this difficult to remove and prone to blocking s trap fitted

Is that from the 2008 / earlier instructions??
 
Status
Not open for further replies.

Reply to Steam from condensate drain in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all Noticed bad smell in my drain out side put my hand down and it unclogged it for now however I checked my sewer drain and after flushing my toilet a good few times nothing is going to the sewer so don't know is there a blockage or what way it works many thanks and advice would be grateful
Replies
3
Views
428
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
5
Views
131
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
5
Views
138
Hi, I have an old steel water mains pipe (approx 45mm) that I need to connect to a new pehd water mains (25mm). I can't get at it to create a new thread so what's the best way of connecting the two? Cheers, Peter
Replies
2
Views
159
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
207
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock