7
Hi,

I have a Warmflow Oil Boiler.

I have noticed that is fires up for a few minutes at random times and then turns off again (when all CH and WH timers are off). I can also force it to do this (again when timers are off) by turning up the thermostat on the boiler itself.

Does this indicate a problem with the actuators? I suspect the Honeywell actuator for the WH. How can I troubleshoot? The valve does sound like it closes properly after WH turns off.

What else could it be? I can't see a frost protection thermostat on the boiler so have ruled that out.
 
Would that be our Danfoss 2 port valve (for the CH) as opposed to the Honeywell valve (for the HW)?

I put a new Danfoss valve on a few months ago as an issue with the switch sticking and heating not turning off - but it was an obvious fault i.e. boiler was on, radiators were on (when timer was off)

This time the boiler only starts for a minute or so then turns itself off (when timer is off)
 
Would that be our Danfoss 2 port valve (for the CH) as opposed to the Honeywell valve (for the HW)?

I put a new Danfoss valve on a few months ago as an issue with the switch sticking and heating not turning off - but it was an obvious fault i.e. boiler was on, radiators were on (when timer was off)

This time the boiler only starts for a minute or so then turns itself off (when timer is off)

Could be that the 2 port valves are closing the circuit okay, but micro switch is on, giving permanent power to boiler.
Danfoss valves very common to do that and the Honeywell valves seem to also be poor quality nowadays.
 
Ok. The micro switch is inside the actuator? So try a new actuator?

Also both actuators connect to a Danfoss programmer which loses time. Could it be the culprit - a faulty clock?

I’d like to try and fix this myself so want to ensure I troubleshoot properly and buy the right parts.

Am I right in saying I’m not losing “a lot” of oil with this issue as it only fires up the boiler temporarily and the thermostat ensures it cuts off.
 
You would need to have the wires checked to see which actuator is putting power to boiler.
You will not use much oil because the boiler will only burn oil to heat itself and boiler stat will cut off power to burner for long periods, if you haven’t radiators or cylinder heating while this happens
 
Top man.
Want to fix it yourself.
What you doing on here then?
 
Top man.
Want to fix it yourself.
What you doing on here then?
Is this not a forum for sharing advice / tips? Technically not by myself ie with the help of this forum - but as opposed to getting a plumber / electrician out unless completely necessary
 
You would need to have the wires checked to see which actuator is putting power to boiler.
You will not use much oil because the boiler will only burn oil to heat itself and boiler stat will cut off power to burner for long periods, if you haven’t radiators or cylinder heating while this happens
So I need to get an electrician out instead of a plumber...
 
So I need to get an electrician out instead of a plumber...

Well somebody that can check and work on the electrics. Most decent heating engineers will be good at electrics.
I am always wary of advising someone to diy electric work.
 
Out of your depth though. Could end up costing more.

That's the end of my free advice.
 
Status
Not open for further replies.

Reply to Oil Boiler fires up for few minutes when timer off in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
1
Views
79
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
93
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
135
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
212
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
232
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock