Is there a required distance that a plastic cold water pipe needs to be from a mains electrical cable. Is an armored cable.
 
Mains cold eg alk or just a cold water pipe internally?
 
I believe there is no proper regulation but the further the better. We do in Germany around a min of 50mm but haven't been there Plumbing for the last 5 years so perhaps changes have been made.
 
From a scan of 17th Edition Amdt 3 Wiring Regulations, there is no minimum clearance from a cold water pipe (regulation 528.3). For gas pipework the minimum clearances are 25mm from a cable to the pipe and 150mm from an electrical switch to the pipe.

For hot water or heating pipework the regulations state: -

'A wiring system shall not be installed in the vicinity of services which produce heat, smoke or fumes likely to be detrimental to the wiring, unless it is protected from harmful effects by shielding arranged so as not to affect the dissipation of heat from the wiring.' - Reg 528.3.1
 
Last edited:
From a scan of 17th Edition Amdt 3 Wiring Regulations, there is no minimum clearance from a cold water pipe (regulation 528.3). For gas pipework the minimum clearances are 25mm from a cable to the pipe and 150mm from an electrical switch to the pipe.

For hot water or heating pipework the regulations state: -

'A wiring system shall not be installed in the vicinity of services which produce heat, smoke or fumes likely to be detrimental to the wiring, unless it is protected from harmful effects by shielding arranged so as not to affect the dissipation of heat from the wiring.' - Reg 528.3.1
I would still stick to the 25mm rule
 
Was going to put a piece of lagging around the pipe were it crosses the electrical cable to try keep a distance.
 
Status
Not open for further replies.

Reply to Plastic cold water pipe distance from mains electrical cable in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock