I have an ancient ch system. Think it's s plan. Fully pumped, open vent, Thorne Olympic boiler.

The old programmer started to play up, so I fitted a Corgi/Tower PR2 2 channel programmer. All went well, until I tried to run it on the programmes I set on it.

The hot water runs according to the programmed times I entered, but the heating won't come on on the programmer at it's programmed times. If I put the heating on constant, it comes on normally wether on it's own or with the hot water if that is already on. It's definitely the programmer that's not switching the heating on at the programmed times, because the three buttons under both heating and hot water light up when the programmer has turned either of them on.

Is the programmer faulty? It's not responding to the programmed times for the heating. Or is there something else? Thanks for any help and advice.

N.B. I have definitely selected 'fully pumped' in the programmer's set up menu.
 
1. Have you checked that the wiring to the new programmer is the same as the old?
2. Have you checked whether there is 240V at the CH motorised valve when the programmer calls for CH heat.
3. Have you checked whether there is 240V at the output from the CH motorised valve when the programmer calls for CH heat.

The normal sequence (with mains voltage switching) is:
a. Programmer calls for CH heat by putting 240V on CH thermostat.
b. If heat required, CH thermostat puts 240V onto motorised valve motor (brown).
c. Motorised valve opens, and when open, puts 240V onto output to boiler. Normally orange.
d. Boiler fires.
 
1. Have you checked that the wiring to the new programmer is the same as the old?
2. Have you checked whether there is 240V at the CH motorised valve when the programmer calls for CH heat.
3. Have you checked whether there is 240V at the output from the CH motorised valve when the programmer calls for CH heat.

The normal sequence (with mains voltage switching) is:
a. Programmer calls for CH heat by putting 240V on CH thermostat.
b. If heat required, CH thermostat puts 240V onto motorised valve motor (brown).
c. Motorised valve opens, and when open, puts 240V onto output to boiler. Normally orange.
d. Boiler fires.

Thanks for your reply.

1. The wiring on the backplate needed to be changed. The old Landis and Gyr programmer had L and N wires plus hw on to term 3 and heating on to term 4. The Corgi needed hw on to 4 and heating on to 6 plus the usual L and N connections.

2.No I haven't checked the 240v when programmer calls for ch heat, on programmed ch times because the programmer says that ch heating is off. When I put it on constant, the boiler/pump come on and heating works normally. The programmer isn't calling for heat at the programmed times - that's the problem. I have to turn the programmer to constant to get ch heating on.

3. As above, programmer not calling for heat on programmed times (heating on lights not illuminated on programmer - nothing from pump/boiler). Only get lights illuminated for ch heat and pump/boiler on if I select constant on heating mode selector.

Sorry it's confusing. I don't understand how I can manually select heating by selecting 'Constant', but the heating won't come on with 'Auto' - even though the programme times I put in are correct.
 
Last edited:
From what you're saying above, I really would be inclined to the opinion that the fault is in the programmer, or simply you haven't figured out how to use it properly. As I cannot see how any other fault in the system, or wiring could cause the programmer itself to fail to call for heat at the right times.

I've just looked at the instructions for that programmer and I must admit it looks like one of those ones that is almost impossible to understand unless you have the programmer in front of you.

This model? : Google

I think you have independent programmes for hot water and central heating, which could be the error?

The manual over-ride are the respective [+1Hr] buttons which should allow you to turn on either function for an hour up to 9 hours (try to select 10 hours to switch back off). Try these and let us know if those, at least, work as they should.
 
F4AD575C-5153-436F-9374-16CB39F10E3C.png

Read 3.1.2 an make sure the programmer is set for the correct type of system you have,makes reference to if it’s in gravity mode the heating will not come on without hot water being on

962AD28B-E679-4391-8CC8-A5EF2007AB4D.png
 
Thanks for your reply. Yes, the programmer was faulty. I took it off and wired it up to just a live and N 240v power supply. The heating would only come on on 'Constant' - wouldn't respond to the timings - which were correctly programmed.

It's fully pumped system and I programmed timer for fully pumped as you mention.

Have swapped for a Drayton, which works as expected. Unfortunately it's not the only problem with this old system, but I have posted another thread.

Thanks for taking the time to help.
 
Status
Not open for further replies.

Reply to Is My New Corgi (Tower) Programmer Faulty? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

It was fitted with the boiler a Potterton Suprima 30L about 21 years ago. Two PCB's later and a new fan the boiler is working perfectly. However, the programmer display is not showing any digits for the clock or anything else so I am unable to program it. It still works the boiler manually...
Replies
14
Views
997
Hi everyone, I’m writing on behalf of my elderly neighbour and hoping this is a problem someone on this forum has experience of and remedied. The boiler was not responding to the wireless thermostat. The various settings on the thermostat seemed fine and 3 heating times and temperatures were...
Replies
1
Views
402
Hi all, I have an OSO Direct 210 hit water cylinder installed in my home, with 2 switches (on/off; and boost). The boiler is for hot water only (rads are electric). In the 5 years that I’ve lived at this property, I’ve never once turned the boiler off; however, with soaring energy prices, I’m...
Replies
6
Views
444
Hi, I am trying to link a Hive heating & hot water dual channel receiver to an old Vaillant THERMOcompact VU GB 242/1 E system boiler. It has an internal programmer that is similar to a time switch 120 (plug in seven day programmer) This programmer is connect to a terminal strip using 345 (three...
Replies
0
Views
401
I have an LG air source heat pump which is controlled by an Optimum Duostat controller This has developed a mind of its own where it ignores the programming So time to swap it out Looking for recommendation for a unit thats easy enough to programme without having 5 time zones Basic time on / off...
Replies
0
Views
375
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock