Hello again – second post, but another plumbing problem – this time about our central heating.

We have a Glow-worm Ultracom 30hxi boiler that feeds our central heating and hot water. It’s controlled by a Drayton Lifestyle controller. The pump is a Grundfos Type UPS 15-60 130 Part number 5952660.

This system was installed before we moved in 2 years ago, so I’ve no idea how old it is, but it’s been working fine until recently.

Firstly, it kept failing with a fault code F25 on the boiler display, which is apparently “Maximum temperature rise slope”. I’d also noted some of the radiators were hardly warm, whereas others were hot. Anyway, I remembered that someone had commented sometime before that the pump was running on setting 3 (maximum), which was over-working the pump, so he’d turned it down to the mid-way 2 setting. I tried putting it back up to 3 and this stopped the boiler faulting on F25 all the time, though there was a lot of ticking noises coming from the pump. All the radiators were then running hot. Anyway, I’d left it running like that for the past 3-4 weeks – no fault codes – ticking noise appeared to stop after a while.

However, in the past couple of weeks, I’ve noticed that the pump is running all night – even when the heating and hot water is off. I got up once at 4am and noted the pump was hot, but all the radiators were cold and the controller said that both the heating and hot water wasn’t on.

To prove this, I set a temperature monitor on the pump for 48 hours and right enough, this showed that the pump temperature was about 45 degrees whilst the heating/hot water was on, but when the heating went off, the temperature of the pump slowly rose up to about 55 degrees, by which time the heating kicked in again, i.e. 5am in the morning.

So why would the pump be running all night and getting hot when the boiler is off throughout the night and periods of the day??
 
If you have an "S" plan system (two separate motorised valves rather than a single 3 port valve) I'd be looking at the auto bypass if fitted. If this were faulty and effectively short circuiting the heating system, this could cause the symptoms you describe.
 
Thanks for the prompt response steadyon. I do have two separate motorised valves that sit just below the pump, but I don't know what the auto bypass is or looks like - or how it can go wrong?
 
After some more investigation last night, I've realised things aren't quite as they seemed in my original post. I'm therefore going to close this post and start afresh.
 
Status
Not open for further replies.

Reply to Central Heating pump on 24/7 and getting hot in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

My central heating is run off a heat pump ( air to water ) quite expensive to run , So I’m plainning to fit a wood burning with a back boiler to connect to the heating system, So while the wood burning on during winter months it will stop the heat pump for working hard Or not all all . My...
Replies
3
Views
235
My son has just had a new boiler fitted and hes noticed that the pump runs 24x7 even when both the heating and hot water are set to off. He’s also found that when the hot water is set to off on the programe timer, the boiler is still heating up water. I wonder if this is because the engineer...
Replies
3
Views
343
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new well maintained Worcester combi boiler. We weren’t convinced the heating was working right and then got hit with a £610 energy bill for the first 6...
Replies
0
Views
248
MartinPod81
M
So a strange conundrum regarding water temp if anyone can help resolve, would be much appreciated. Ive tried to give as much info as possible to give a full picture but let me know if ive missed anything. I have a Baxi Avanta 25h heat only boiler. Works fine. Unvented 300ltr megaflow. Stated...
Replies
1
Views
146
R
Hello its my 1st post hope im in the right place We brought a new house a medium-large 3 bedroom semi, we moved in the summer. Now coming to winter we started putting the central heating on. The central heating has a mind of its on it’s really strange iv never experienced this We put the heating...
Replies
1
Views
403
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock