hi,

Ok so have a 4 bedroom house.

Vaillant System boiler 637

No rads just underfloor heating. 3 x manifolds and nothing too big.

UV hot water tank.

Client complained that UFH has never worked properly.

I found system to be surprisingly dirty. Pumps knackered.

I replaced all manifold pumps, pump on boiler, removed actuators, replaced balancing valves and flow meters. Through all of these steps it always produces a new problem.

The issue I have is that the boiler keeps cutting out. Apparently it’s noticibg to small a differential temperature on flow and return. I’ve added a bypass to system which hasn’t helped. It will ramp up to 70 when asking for 60 and cut out. There’s no restriction on the system and Vaillant can’t give me an answer. Seems as though heat exchanger ok, but thing won’t stay lit. I’m at wits end. I understand that UFH has never known to work by client so I’m in the clear there but really do t want them to spend all this money and I can’t get it up and running. If anyone can help me brainstorm this one I’d be much appreciated.
 
Boiler is to big how is it piped a low loss header ? you could try down rating the boiler its in the installation manual how to do this or ring Valliant technical they will talk you through it i would try 24kw this is enough . Do you have zone valves and a auto bypass valve at the UFH manifolds the heating load needs somewhere to go even if it modulates right down the boiler needs the facility for pump over run , sounds like a design fault put some pictures up bud .Cheers kop
 
:(Note to one self, read OP’s post properly
 
Last edited by a moderator:
What make is the manifold, in fact pictures would be better.?

Lots of pics, pipework at boiler any valves, manifold etc.
 
Hi,

Have tried down rating at quite a few different kws. Currently at 12kw but no help.

It’s a polypipe manifold and have spoken to them but no help.

Hot zone valves at each manifold. 1 bypass internal to boiler and additional bypass near to boiler.

Will try and attach some pics on laptop when I get home as can’t work it out on phone.

I was thinking low loss header the only way forward but really want to give customer a difinitive answer.
 
Does it look like this manifold?

828939D0-89D3-4F79-8239-108076AF417E.png
 
If it does, have you removed the filter from the top and checked for debris?
 
Status
Not open for further replies.

Reply to CANT GET UFH to work!!! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi Everyone I wasn’t sure whether to post this in here or UFH but hopefully I’m posting this in the correct group. I’m in the throes of a full renovation and am currently designing the central heating system, I’m installing radiators (11 or 12 in total) and am going to run each rad from its...
Replies
7
Views
735
G
HI folks, is it possible/feasible/reasonable to insatll an ufh manifold and system (for a 17m2 room) from a disused CH 15mm flow and return? I would install a 15 to 22mm reducer into a pump then a 2 port manifold then into the floor then. back into the return of the manifold. Its an old...
Replies
2
Views
522
Do people with this type of mixed flow temperature control have any problems with achieving the required manifold flow temperature? The one below I think is similar to the TIO Mixing unit. In the unit below, the hot (boiler) water enters from the bottom left, red arrow, up through the "mixing...
Replies
3
Views
515
Good morning, wondered if anyone can advise please on a resolution? My set up at home is that I have a 4-bed detached with 21 radiators (includes 4 towel rails), a 6m x 4m orangery/conservatory that was built last year with under-floor heating, and a Megaflo for storing hot water. The UFH...
Replies
61
Views
5K
I am doing heavy house renovation and want to have ufh (multizone) at the ground floor and radiators on upper floors. I want to have consistent controls, with manifolds feeding both the ufh loops and radiators, and the same type thermostats controlling both (depending on the room, the...
Replies
3
Views
949
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock