Discuss Condensing Boilers - what volume of codensate is discharged in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Rob Foster

Esteemed
Messages
2,083
When a 25 kw condensing boiler is going full tilt in the winter what volume of condensate water might be discharged per hour ? Obviously an overflow pipe will cope. Anybody any ideas. It could be 20KW or 30 KW I am looking for a ball park volume. Many thanks
 
Types of work ....1 Contract ch installation new build, 2 medi-gas contracting, 3 local plumbing/domestic ch installs but in a quite tight area - no adverts just word of mouth so we knew the customer and they us. 1st 2 profit is all down to margins and speed 3 is down to reputation word of mouth. Beware you have to get from one man (you) to over 5/6 very quickly or you end up not earning anything yourself Young men for 1, steady fellas for 3 and anybody who was prepared to work xmas easter and bank holiday for 2
 
Hi fixitflav thanks for that - how did you calculate it may I ask - in awe of you on this one
Originally I used a hand calculator and seem to have dropped a cod, it's actually more like 3.8 l/h.
Calculation below. I used Mathcad, but pleasantly surprised it copied in OK. Don't worry about apparent lack of conversion factors etc, Mathcad takes care of that for you. I've made one or 2 assumptions, as natural gas is not pure methane, but it won't be far out for water produced. Be interesting to compare with maker's figure, to get an idea about what fraction condenses. Come back if you need more.

upload_2018-8-7_19-17-40.png
 
Originally I used a hand calculator and seem to have dropped a cod, it's actually more like 3.8 l/h.
Calculation below. I used Mathcad, but pleasantly surprised it copied in OK. Don't worry about apparent lack of conversion factors etc, Mathcad takes care of that for you. I've made one or 2 assumptions, as natural gas is not pure methane, but it won't be far out for water produced. Be interesting to compare with maker's figure, to get an idea about what fraction condenses. Come back if you need more.

View attachment 34144

2.347m3/hr not 2.429

also that figure is a constant 25kw on a heat/system boiler which even at the middle of winter wont run constantly on full

if its a combi that figure will be lower also due to the output
 
Depends on the makeup of the gas and the assumed boiler efficiency, but either is near enough in practice.

OP said "when the boiler is going full tilt".

Yes but I would be surprised if it went for longer than 30 mins on full tilt will modulate down to half power

Also return temp matters a lot
 
Rob, when you had 20 fitters working for you what sort of work were you doing?
Rob, when you had 20 fitters working for you what sort of work were you doing?
I did not mean to end up with 20 or so. I had semi retired at 40 ish , myself and 2 others did really well in the late 80's + 90's building and property. I was stood in a pub ! fella next to me was doin xword and asked whats a greek cheese ? conversation ended with him asking me to help him with a ch installation next day. When we did it he was impressed and asked how much I wanted - I told him - Jimbo said he didnt earn that rate himself. So it ended up with me getting the work for him and about a score of his really experienced older pals at my idea of rates - it worked. wacky story but all true
 
Yes but I would be surprised if it went for longer than 30 mins on full tilt will modulate down to half power
So would I, but my calc is for an instantaneous rate. Reminds me of introduction to rates of change and differential calculus a few (!) years ago. Sir told a tale of a woman being stopped by a cop and told she was doing 45mph. Don't be silly, officer, she said, I only bought the car 10 minutes ago.
Just out of curiosity, how do you get 2.347m3/hr in #12?
 
So would I, but my calc is for an instantaneous rate. Reminds me of introduction to rates of change and differential calculus a few (!) years ago. Sir told a tale of a woman being stopped by a cop and told she was doing 45mph. Don't be silly, officer, she said, I only bought the car 10 minutes ago.
Just out of curiosity, how do you get 2.347m3/hr in #12?

25/10.65
 

Reply to Condensing Boilers - what volume of codensate is discharged in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi All, My home is 2 storey - split into 2no zones. 14 rads downstairs and 7 upstairs. Open vent system standard boiler. Hot water is immersion heater. The old boiler was a worchester bosch dansmoor rated at 26-32kw. Nozzle spec was 1.0 gph. However the enginer had 0.85gph nozzle in it. It...
Replies
17
Views
2K
    • Love
Recent install Firebird 26kw Condensing boiler. Space heat only. Installed as replacement boiler in well insulated 80s renovated home. (Silver bead wall cavities, triple glazing 0.6 centre pane U value, 450mm rockwool in loft) This house is now split into 2no zones. Downstairs and Upstairs...
Replies
186
Views
14K
Hello everybody! I have little issue, and hope you will be able to help: I have very old oil boiler on conventional system. What happens is: When i turn central heating on, boiler is heating for about 1 hour, what happens at the end is pipes sound really loud(loud crackling sound) and overflow...
Replies
1
Views
938
I live on the 3rd floor of a 6-story block of flats. (26 flats in total). During the evening when all people are inside their flats and using their boilers to heat their flats, there is obviously lots of steam coming out of all the different Boiler Flue Vents. if I open my window or go outside...
Replies
1
Views
1K
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm. This question is for my own house setup. We are really fortunate to have a large house, about 5,000sqft in total over 3 floors. It was built around...
Replies
9
Views
1K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock