Search the forum,

Discuss UFH heating problem - No manifold in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
2
My builder has fitted the UFH piping and then the screed and flooring but has not put in a manifold - What can we do? Can we just hope that the system works when the manifold is fitted? Obviously we don't want to tear up the floor and screed?? I've read it should have been pressure tested and the manifold fitted prior to this? To compound matters...the builder has now done a runner..so we are looking to someone else to finish off our build
 
Any pics ?
 
All the pipes run up into a cupboard ready for the manifold. Trouble is he’s already installed Amtico flooring....can we just get the manifold installed and hope that all is ok? Eg. I don’t want to contemplate ripping up floor and screed unless we have to

2E6FC347-20F4-459A-BF5F-8C3885FAEB9E.jpeg
 
You will need to fill and flush out the heating loops under the floor and pressure test the pipework before fitting a manifold and pump set . Cheers kop
 
I would pressure test the pipework before doing anything
 
I would set a static air pressure test - 2 bar- so if it does leak badly no water in wrong place then if it does or does not leak air let us know and we can advise you more.
 
058471EC-0511-47E3-AEB2-1BA6A03F92AE.jpeg
Sorry. It needs a manifold and connecting into the main Heating primaries also the floor should have been commissioned and dried before your amtico went down.

Heres one from earlier this year. Floor still had moisture in it.

7EB6B55B-C481-422C-B979-C4B161806D6B.jpeg


D96493AF-ADBD-4653-A0B8-0AE2748B2269.jpeg
 
I would set a static air pressure test - 2 bar- so if it does leak badly no water in wrong place then if it does or does not leak air let us know and we can advise you more.

Can't air test above .50 bar
 
You could use a regin type pump to put 1bar pressure in there first but no more! if your worried about leaks , but nothing beats a water hydrolic test and you need to make sure you have a flow and return with a good flow in and out and the pipework is not blocked and is leak free this will save you a lot of grief further down the line now Bodge it and Leggit has moved on to his next victim. All the best kop
 
Why is that then ? would 0.5 bar do then ? use a moded up drainage balloon or pump

Because it could kill someone if a fitting or the pipe pops

Due to air compression
 

Reply to UFH heating problem - No manifold in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock