Discuss Buffer Tanks - 2 or 4 port connections in the Plumbing Jobs | The Job-board area at PlumbersForums.net
As Worcester said you could use the hot water module on the buffer and pipe the boiler direct to the buffer and come out the other side to your heating. You then add the middle sensor to help monitor the buffer charging status. Difference between the two schematics you've shown is the ETA shows a shunt circuit with mixer valve, the Froling does not.
We have always used the 4 port buffer system, we set top of buffer to 80 min with 5 deg hysteresis and bottom off at 70 deg. We find that the systems are never short of heat as the buffer is always already 70% charged and boiler only fires using buffer sensors only.
we have taken out quite afew biomass boilers from schools, but when you looked at the system, they were never designed correctly and tbh, the boilers were s~*t, but 10 years ago we didnt know any different. we have replaced some of these boilers with new ones, altered the systems and controls, and had them accredited to Rhi which makes a huge difference to them - and now they are much happier using them.
i just think there wasnt enough technical knowledge in the uk about biomass back then!
The other issue is staff not wanting to get dirty clearing the ash. One site the caretaker said it wasn't in his job description to clean out the boiler!
im sure something can be made so it dumps the ash into a galv bucket and the site manager (caretakers new job description ) empty's/ spreads on garden
A buffer, volumiser, accumulator, thermal store etc should only be fitted as a last resort as they only add to the heat load, add a lot of cost to the install and lose heat for a past time.
If the boiler modulates or good control can be added to avoid cycling then that's the way to go.
A buffer, volumiser, accumulator, thermal store etc should only be fitted as a last resort as they only add to the heat load, add a lot of cost to the install and lose heat for a past time.
If the boiler modulates or good control can be added to avoid cycling then that's the way to go.
Buffer and boiler sound way to small ...
Sounds like they should have done it all on gas from the beginning
As anyone done a proper hourly heat demand calculation over a 7 day and monthly profile?
It was an absolute joke. The peak heat load worked out they say at nearly 1.6mw, and part of the agreement is that the biomass boiler covers 70% of that. No chance!!!!. Then they reckon the heat loss over the whole system being in mind there is 230 hiu's, all pipework above and below ground is 5" steel, is only 8%.loss.which is to be taken on the chin in our price. We reckon the heat loss will be nearer 40%. And the flue!!!!!, 250mm, no fans other than the draught fan on the boiler, has 4x 90 degree bends, and then runs up the side of the flats for 18 floors.
View from across the pond....
https://blog.heatspring.com/2-pipe-versus-4-pipe-buffer-tank-configurations/
Cooling of the flue gases with such a large external run would be my concern, condensation etc. Although being an induced draft I'm not entirely sure if I'm honest.
The sizing tends to suggest that the biomass is to cover a base load ( buffers to smooth out and absorb heat main losses) with the gas boilers ready to fire for peak demands, hot water etc. I'd be interested to see the design calculations.
Where did you get the heat load figures from? 8kw for a flat seems high. 37kw to hot water would give a flow rate of approx 13-14ltrs/min. Even running a bath would would only require a demand at that rate of approx 5 mins.
The Council won't have its own heating experts and will have appointed a consultant to advise them, it would take a heck of a lot to admit that the consultant was wrong.