Search the forum,

Discuss Baxi Bermuda 50/6 Lockout Problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Messages
1
Baxi Bermuda 50/6 causing me a problem

When calling for heat the boiler just goes straight to lockout with a solid red light at front on PCB and an orange light flashing twice at rear

19 mBar at the gas valve

Pump starts and works fine

1.6k Ohms and 3.8k Ohms across the gas valve

12k Ohms at 22 degrees across the sensor

Potentiometer 0 - 8k Ohms

All appear to be approximately corresponding with MI's

Replaced the PCB - no change

Replaced gas valve - no change

Replaced potentiometer - no change

Now I am stumped - So would appreciate any of your experience, knowledge or suggestions of what else I could try / test

Edit: GSR but not sure where to submit my details
 
You'll need to increase your post count up to 10+ then send a message to [email protected] with a picture of your gsr card, front and back.

We do not discuss the repair of gas appliances in open forum.
 
Status
Not open for further replies.

Reply to Baxi Bermuda 50/6 Lockout Problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock