  1. Tyrone Edwards

    Tyrone Edwards New Member

    i have an Ideal Espirit 2 boiler, the water is working perfect but the heating is not working.
    We had a new pump fitted about 12 months ago, I've had three tradesman in and they have all said sometime different; one said I needed a new pump the other said I needed a new programmer and the third said I needed a new boiler.
    I'm sick of being ripped off, can someone please let me know if they have any idea what the problem could be
    Thank you
     
    • Like Like x 1
  2. Harvest Fields

    Harvest Fields Trusted Plumber GSR Top Contributor!!

    What do you mean by not working. Can you please supply more information.
     
    • Like Like x 1
  3. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    Ideal have a fixed price repair, if your stuck
     
    • Like Like x 1
  4. Tyrone Edwards

    Tyrone Edwards New Member

    As mentioned the water is working fine, the thermostat is bluetooth, the pump does not even fire up
     
    • Like Like x 1
  5. Tyrone Edwards

    Tyrone Edwards New Member

    I do know before we had the pump replaced, the iprogrammer got wet, the digits still show up so I assumed this to be fine
    Could this be the issue?
     
    • Like Like x 1
  6. Harvest Fields

    Harvest Fields Trusted Plumber GSR Top Contributor!!

    What programmer is it?
     
    • Like Like x 1
  7. Tyrone Edwards

    Tyrone Edwards New Member

    It's the Esprit 2 35w - itime programmer

    IMG_0852.JPG
     
    • Like Like x 1
  8. jtsplumbing

    jtsplumbing Plumber GSR

    Is boiler showing any fault code ?
     
    • Like Like x 1
  9. Tyrone Edwards

    Tyrone Edwards New Member

    There's not fault code showing
     
    • Like Like x 1
  10. jtsplumbing

    jtsplumbing Plumber GSR

    Well as its working for hot water that means your Pump is OK, these did have problems with the control panel, but other things need to be checked on heating side not allowed to go into to much detail ! what did the other people check when they looked at your boiler ??
     
    • Like Like x 1
  11. Harvest Fields

    Harvest Fields Trusted Plumber GSR Top Contributor!!

    Random question but your thermostat is turned up isn't it?:p:p:p;);):)
     
    • Like Like x 1
  12. Tyrone Edwards

    Tyrone Edwards New Member

    I’m not sure what was checked, other than three different options, I’ve purchased a new control panel which should be here Monday, if that doesn’t fix it then I’ll replace the bluetooth thermostat.
     
    • Like Like x 1
  13. Tyrone Edwards

    Tyrone Edwards New Member

    I knew there was something I didn’t do
    I’ve bought a new control panel which I’ll fit Monday and see what happens.
    I’ll post the results
     
    • Like Like x 1
  14. dan_the_plumber

    dan_the_plumber GSR

    Sounds like external controls at fault. Simple test is to pull message wires out and put a link in. If programmer/stat at fault, your boiler should now run constantly on a heating demand
     
    • Like Like x 1
  15. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    FYI you need to be gas safe ;)
     
    • Like Like x 1
  16. Tyrone Edwards

    Tyrone Edwards New Member

    I’ve fitted the new itime programmer and still no heating :mad:
    Next step replace the Bluetooth thermostat, does it have to be a specific thermostat or can I buy any one?
     
    • Like Like x 1
  17. Harvest Fields

    Harvest Fields Trusted Plumber GSR Top Contributor!!

    I do not think that the timer you have shown is Bluetooth? Do you have a receiver to go with the thermostat. If so can you post a picture. Cannot remember what you said in you previous posts.
     
    • Like Like x 1
  18. Jane Carter

    Jane Carter New Member

    I think it must be the problem created by the radiator.
     
  19. jtsplumbing

    jtsplumbing Plumber GSR

    Think what he has is a RF room stat not Bluetooth ! why is he messing around replacing parts that may not be faulty, any decent engineer can soon tell if the RF unit the problem,
     
  20. Harvest Fields

    Harvest Fields Trusted Plumber GSR Top Contributor!!

    That’s where I was getting. To mate. Probably external controls all along as somebody said in a previous post.
     
  21. Tyrone Edwards

    Tyrone Edwards New Member

    I’m not an engineer, I have had three different heating engineers look at this and they have all told me a different reason for the fault. The prices they have quoted to repair were stupidly high
    This is a picture of the heating controls, apologies if I have given any wrong information previously,I am just trying to find an honest engineer, which is proving to be difficult

    90B1BB03-0FA0-4363-95ED-58B1869E751A.jpeg

    403071A0-3740-451C-9EAB-54DD2D33C4A0.jpeg
     
  22. Tyrone Edwards

    Tyrone Edwards New Member

    Decent/honest engineer? Easier said than done
     
  23. Harvest Fields

    Harvest Fields Trusted Plumber GSR Top Contributor!!

    Decent engineer are hard to find that’s why we say on here gonfor someone that is recommended to you. Is the light not the right of the receiver orange or red?
     
  24. ShaunCorbs

    ShaunCorbs S. Mod Trusted Plumber GSR Top Contributor!!

    That stat is rubbish replaced a few the range isn't what it's listed at try less than half
     
  25. Tyrone Edwards

    Tyrone Edwards New Member

    Does anyone have an idea of the rough price to remove the external stat and wire up to to main programmer
     
    • Agree Agree x 1
  26. jtsplumbing

    jtsplumbing Plumber GSR

    Depends how far cable needs to run ! But more than likely the RF receiver is faulty but has B4 its very easy to check , Cost to replace RF room stat would Proberly be around the same price has hard wiring one in, What prices have you been given ??
     
  27. Tyrone Edwards

    Tyrone Edwards New Member

    I’ve not been given a price as yet, wanted to check on here what a rough cost would be, was quoted £350 for a new itime programmer, bought and fitted that for £130.
    The RF is less than one metre away from the unit, I just want it disconnected then reconnected to the itime programmer
     
  28. jtsplumbing

    jtsplumbing Plumber GSR

    To replace the RF room stat & receiver is something you could do yourself as you don't need to get into the boiler, if you can do basic wiring it fairly straight forward, shop around for price or replace like for like
     