Hi All,

Bit clueless here, but wanted some advice if possible.

We had a new 200ltr unvented system installed recently. All seemed fine, however the CH kept turning off and rads going cold.

I checked the EV in the loft, and it's pressure gauge had dropped to 0. I opened the valves up and filled back up to 1.5bar (on advice of the fitting plumber). This got the rads going again, but two hours later it's back to no pressure/rads off?

When the rads came back on originally, I could hear them bubbling away (filling up?) quite loudly. I bled them, two released air...

The only thing I've done recently since the install is turn the gauge on the Worcester boiler up from 1/2 way to full.... could that be a problem?

Overflow seems fine, no water came out the EV when I checked...

Plumbed said air possibly escaping the system somewhere, or water leak in the ground floor pipes, but could try a sealing solution.

He's v.good, but is there anything obvious I should look for/try before rushing them back out? It seems a bit extreme the EV drops pressure in two hours?

Thanks,
CN
 
What size vessel is it? and how many radiators are there? Also the higher you set the temp on the boiler, the more expansion there will be in the radiators.
 
What size vessel is it? and how many radiators are there? Also the higher you set the temp on the boiler, the more expansion there will be in the radiators.

Thank you for the reply!
I'll have to get up into the loft and have a look in the morning to see the size, i'm unsure myself.
There are only 7 radiators in the house. I've turned the boiler down now and also will turn the thermo down in the living room.

Could this possibly be a cause for draining the pressure?
 
Is the new UVC the only work you had done relating to the htg system?
 
Is the new UVC the only work you had done relating to the htg system?

Hi, yes.
There were some other things associated with it, like a new pump as the old one was clogged up (that's set to max setting), 2 number 2 valves, moved some electrical work about (the control panel went from the tank on 1st floor to ground floor), but nothing else.
UVC was put in now in prep for a new bathroom strip out and install.
 
Where is the boiler now? When you look outside, there should be a discharge pipe for the boiler. Is the wall wet or stained below it? Once you've re pressurised, does the boiler pressure gauge rise a lot more - into the red or to say 3 or 4 bar?
 
Hmm. Pump up to 3 to get CH going!! Over to you HF end of my knowledge... but sounds somewhat odd...
 
Where is the boiler now? When you look outside, there should be a discharge pipe for the boiler. Is the wall wet or stained below it? Once you've re pressurised, does the boiler pressure gauge rise a lot more - into the red or to say 3 or 4 bar?

Boiler is in the utility room. I'm not v.experienced with this sort of thing. I went outside hoping to see a pipe dripping or a wet wall, but the only thing I had in a protective case was a black pipe pointing up, not down as I'd expected.

I havent looked at the boiler in the utility room once i'd pressurised the EV.
 
Hi @jtsplumbing - I've attached two of the black pipe that comes out of the boiler/utility room.
Hope it makes some sense to you, I have no idea with plumbing at all, so it's like trying to speak Dutch :oops:

IMG_7859.JPG


IMG_7860.JPG
 
Hi All,

Bit clueless here, but wanted some advice if possible.

We had a new 200ltr unvented system installed recently. All seemed fine, however the CH kept turning off and rads going cold.

I checked the EV in the loft, and it's pressure gauge had dropped to 0. I opened the valves up and filled back up to 1.5bar (on advice of the fitting plumber). This got the rads going again, but two hours later it's back to no pressure/rads off?

When the rads came back on originally, I could hear them bubbling away (filling up?) quite loudly. I bled them, two released air...

The only thing I've done recently since the install is turn the gauge on the Worcester boiler up from 1/2 way to full.. could that be a problem?

Overflow seems fine, no water came out the EV when I checked...

Plumbed said air possibly escaping the system somewhere, or water leak in the ground floor pipes, but could try a sealing solution.

He's v.good, but is there anything obvious I should look for/try before rushing them back out? It seems a bit extreme the EV drops pressure in two hours?

Thanks,
CN
Sounds like the diaphragm in the pressure vessel could be ruptured. What happens then is that there's nowhere for the expansion when the system heats up so it dumps the excess pressure through the pressure relief valve to outside. When the system cools down the pressure also goes down with it usually to zero thereby shutting down the boiler. The easiest way to check is to poke a small screwdriver in the schrader air valve (like a car tyre valve) on the expansion vessel and push it in. if water weeps out of it, the diaphragm has ruptured.
 
If you press the pip down on the expansion vessel and water comes out, the expansion vessel is knackered.
If not, pump expansion vessel back up to system pressure (typically 1.0 bar)
The Shraeder air valve on the expansion is probably loosing air. You can buy a Shreader valve extension tube from city plumbing for ÂŁ11.00. Stick that on, it's like replacing the valve effectively. Job done.
It is probably an engineer job though, since there are a few finaties, draining the boiker etc.
 
If you press the pip down on the expansion vessel and water comes out, the expansion vessel is knackered.
If not, pump expansion vessel back up to system pressure (typically 1.0 bar)
The Shraeder air valve on the expansion is probably loosing air. You can buy a Shreader valve extension tube from city plumbing for ÂŁ11.00. Stick that on, it's like replacing the valve effectively. Job done.
It is probably an engineer job though, since there are a few finaties, draining the boiker etc.
Just because there is fluid inside the vessel. It does not necessarily mean the diaphragm has gone. Sometimes condensation builds up inside the vessel and just needs to be drained out.
 
Hi All, just to update you following your comments, the plumber came back out, released air from the pump he'd installed, switched all bleed valves around to make it easier to bleed and took all air out of the system, recharged it all and added 3 tubs of sealant to the system. Appears to have done the trick thankfully!
 
Just because there is fluid inside the vessel. It does not necessarily mean the diaphragm has gone. Sometimes condensation builds up inside the vessel and just needs to be drained out.
Never heard of that before. How does the moisture get into the air side of the vessel to begin with?
 
No idea. But I have drained a few and topped them back up and never been back to change one even though I have serviced them.
 
condensation is water vapour suspended in air until it is cooled below it's due point. At which time it becomes water. Granted this may happen if your expansion vessel is in an unheated area, but not in any great quantity.
Membrane or to give it its full name 'Impermeable Membrane' is not permeable. If it were it wouldn't be very good at its job.
A far more plausible cause of water on air side of membrane would be a small hole in membrane or compromised seal.
Also not ever being called back to an address is not evidence that your original repair was successful, in fact you may find it to be quite the opposite.
 
condensation is water vapour suspended in air until it is cooled below it's due point. At which time it becomes water. Granted this may happen if your expansion vessel is in an unheated area, but not in any great quantity.
Membrane or to give it its full name 'Impermeable Membrane' is not permeable. If it were it wouldn't be very good at its job.
A far more plausible cause of water on air side of membrane would be a small hole in membrane or compromised seal.
Also not ever being called back to an address is not evidence that your original repair was successful, in fact you may find it to be quite the opposite.

Have a read of the process of diffusion of water through solid substances
 
I've looked that up. An interesting concept. Although in my opinion wouldn't lead to much water being on air side. Maybe a bit but, generally if you've got more than a squirt coming out the Shraeder then your vessels knackered.
 
Never heard of that before. How does the moisture get into the air side of the vessel to begin with?
When they are recharged with a foot pump water goes in with the air depending on humidity. Think they're filled with nitrogen from new and I have read that if nitrogen leaks out then replace vessel?!?
I have always pumped them back up and not had problems.
 
Status
Not open for further replies.

Reply to Expansion Vessel losing all pressure in hours? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock