Hi All,

This is my first ever post as a newly registered gas safe engineer. I’m looking for help on an issue I tried to help with for an old couple that live locally to me.

They have the above boiler and very recently have had constant issues with it kettling and almost immediately locking out. The pump was very weak so I’ve replaced this for them thinking the issue was circulation and the new pump would resolve the issue.

As I’m posting here it’s needless to say that the issue still remains!!! Plenty of flow through all the rads and the cylinder but still the boiler ignites and locks out immediately. I’ve bled the whole system and bled the bleed pips on top of the flow and return pipes to the boiler, all good.

I’ve suggested that the heat exchanger may be blocked and they would be better off now getting Baxi in for a one off fix.

Is there anything else I should have done for them? I’ve handed them over to Baxi and admitted it’s beyond me at this stage, but for my own knowledge and experience could it be anything else?

Thanks for any help.

Mike.
 
Here’s the old pump.....

63CB7D6A-34D7-4534-8B35-2F65C938DF32.jpeg
 
correct! It is indeed the valve that is still attached to the pump, I replaced the unions also

Thanks very much for the welcomes!

Agree, the system does look as though it’s not been cleaned for a while. The old boy reckons he did have it flushed a couple of years ago though. Unfortunately he’s since had a stroke and is bed bound so can’t give me much more info. His wife is also losing her marbles, I just don’t want them getting ripped off.
 
Or me handing them over to Baxi when there’s something I’ve missed...
Baxi may fix it but will their one off repair charge include the heat ex if needed? I know some manufactures exclude this from their one off repair service.

Also if the system is as bad as it looks they may refuse to repair it until the system is properly cleaned.
 
Yes, according to the bloke I spoke to on the engineers helpline.

If not I might suggest I flush the whole system rad by rad and put a new boiler in. The boiler hasn’t been maintained by the looks of it, condense trap was rammed.
 
Yeah I agree, how can I determine if it’s the heat exchanger or a blockage elsewhere...it’s a large detached house so a power flush is going to cost them the same as the £340 Baxi want.

Thanks for all the help everyone, really great forum
 
Mmm, great idea with the magnet, thanks. The pump is in a kitchen cupboard downstairs, I can hear and feel good flow through the cylinder upstairs and all rads which is baffling me and draws me back to the conclusion it’s the boiler....

I’ve got until tomorrow night to suss it out and cancel Baxi who are coming on Friday
 
If you have good flow, then it would circulate. I would say that you have a serious blockage, either in the hex or is there a filter on the return? Is there a mag filter? If so, it could be “full” or a valve turned off
 
Will go back and have a look tomorrow, no valves will have been touched as he’s bed bound and his wife can just about boil a kettle, bit of a sorry situation!!

Thanks again everyone.

Mike.
 
Had something similar a while ago on a ideal classic . Changed the pump no different flushed out the rads which were all like tar inside no different. Added system cleaner no different turns out the the blockage was around the vent cold feed and first pump isolation valve from all the crap out the boiler which was rusted up and broke in to bits so new boiler installed
 
There was a Fernox filter on the system, it was dirty with sludge but wasn’t impeding the system too much I wouldn’t have thought. Gave it a clean out but still the boiler locks out.

Over to Baxi now so fingers crossed I’ve not wasted the couples money, I’ll keep you updated.
 
I am not particular familiar with the HE (I stopped being SE some years ago), so excuse me if any if the following is irreleavant.
Is this the one with the diagnosis lights? What do they say?
Is their an overheat sensor?
Is this a sealed system or header tank? if a header tank, then take a magnet and test for magnetism at the junction if the cold feed to the system. If magnetic, then remove that section of pipework and clean/replace.
 
Just a thought for you the flow switch top right of the boiler could be at fault I had this happen when I replaced it the main heat ex became completely air locked so I linked it out temporary which then made boiler fire removed all air boiler then worked a dream this was what baxi them selves told me to do might be worth a look link out old flow swit h to test first.
 
Thanks all - Baxi came out yesterday and have said that it’s not the boiler. He replaced the seals on the combustion chamber thinking they were leaking heat and setting the overheat stat off but still no joy. He said it’s on the system somewhere. I wasn’t there when they attended so can’t confirm if he checked the flow switch but would assume he did!?

I feel a bit guilty as I was certain it was the boiler, but it must be a huge blockage somewhere on the pipework so I’ll get back there ASAP to try and locate it - will start with the feed and vent connections as previously suggested.

Thanks again everyone, really impressed with the forum, I’ve steered clear of (certain) forums for such a long time due to some negative people, but this is far different and appreciated.
 
Last edited:
Thanks guys, I checked the wiring when I replaced the heating 2 port head, they’re both opening up fine as I’m getting good flow upstairs, certainly through the cylinder in the airing cupboard as I can feel and hear it.

Blockage must be on the return I can only assume. I’m going to put some chemicals in the filter and run it cold for a few days, see if that frees anything up.
 
Thanks guys, I checked the wiring when I replaced the heating 2 port head, they’re both opening up fine as I’m getting good flow upstairs, certainly through the cylinder in the airing cupboard as I can feel and hear it.

Blockage must be on the return I can only assume. I’m going to put some chemicals in the filter and run it cold for a few days, see if that frees anything up.

You keep saying you are getting "good flow". If there is "good flow", then by definition there is not an actual blockage.

The OHS is tripping. Therefore there is poor circulation. Suggesting a blockage. Ergo there is not "good flow". I fear that your perception of good flow is clouding your judgement, and causing you to assume too much.

Did you check the cold feed connection (assuming a header tank). this is by far the most common cause of this problem, in my experience. Sticking cleaner in a system with zero flow is probably a waste of , labour, time and cost.
 
My apologies, I’m not using the correct terminology. I mean that the pump is working well (I have changed it) and there is flow up to a certain point in the system, by good I mean that in the cylinder cupboard there is flow from the pump up to this point. So the blockage must be elsewhere. There is a header tank yes.
 
I’m confused. When you say circulating can you prove the water is moving? Are the pipes getting hot? Or are you just feeling vibration through the pipes
 
My apologies, I’m not using the correct terminology. I mean that the pump is working well (I have changed it) and there is flow up to a certain point in the system, by good I mean that in the cylinder cupboard there is flow from the pump up to this point. So the blockage must be elsewhere. There is a header tank yes.
How do you know?
What are the flow and return temps on the circs?

Sorry, M, no one is trying to trick or belittle you. Are you new to plumbing, or just to Gas Safe? As per LP, how do you know there is good flow, as I thought no heat is leaving the boiler? You cannot "feel" the flow, apart from assesing temperture rises either by your hands or thermometer. You may feel some vibrations, but that does not mean water is circulating. You need to start from basics. the boiler is tripping on the 'stat (Yes, apparently). The 'stat is reacting to a rise in temp (sometime the stat or connections can be faulty, but in thos case you are reporting kettling (which, BTW, it probably isn't, it is overheating, which is slightly different), so we know the temp is raising at the boiler, evidencing that the stat is doing its job). That bit tells us there is a circulation problem - some sort of blockage/restriction. The fact that you have no heat to rads or hot water tells us that the problem is before the motorised valves or after the junction of both circuits, forming the return. (Do not start removing rads as per one of your early posts, that is a waste of your time.) The list of available suspects now becomes very limited. It boils down to: air, sludge or scale, or a valve

Air: are there any manual or Auto Air release bleed valves on a high point. Typically immediatly above the boiler, or in the A/C. AARV are notorious for sticking or leaking. Quite often, they are connecte with a compression nut - so you can carefully unscrew the nut below the valve to check for water/air

Valves: These are often inadvertently turned off, (or turned off, back on again - but without the spindle turning. Often a punter in a blind attempt to sort a problem will try various knobs) so you need to check. (I am aware this seems unlikely due to the occupants, but could a "freind" have been trying to help?

From experience: If there has been DEFINITELY no prior attendance by an "engineer", the A/C will be the location of such a valve problem, If there has been another "pro" in attendance, look at the F&R valves on the boiler. This is a prime area for a lever valve to be apparently in the correct position, but the valve being stiff locks in the closed position. A bit of effort moves the plastic lever, but leaves the valve closed. the same applies to Mag Filters.

Sludge or scale:. This, to the extent of a complete blockage, is actually very rare: I cannot recall seeing it occur, (on a heating system) TBH. EXCEPT (at a grave risk of being accused of repeating myself, at the junction of the cold feed and the system - have you checked this???)

You must relax, stand back, and apply logic. Talk to the occupants, (more often than not, I can ask 5/6 questions and be confident where the problem lies), but be aware that they are sometimes stupid, and sometimes lie :)

Years ago, I fitted a sytem in a "standard" house that was being renovated. Ages later, I was told a bedroom rad was slow to heat. I could not work out what the problem was, but it was no major issue. Until another worker lifted a floorboard, pulling out a nail that somene had hammered in (obviously never having heard of "pipes in the centre, nails on the edge"). It presented enough of a restriction to reduce flow to that rad, but had NEVER apparently leaked. Looking back, if we were all concerned enough to find the problem, logic would have forced us to find the problem.

Good luck
 

Reply to Help with a Baxi Solo 30 HE Regular in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all, can someone get to the bottom of this before I call a plumber, en suite shower started leaking from the mixer bar so took the shower off...
Replies
2
Views
602
I have a very strange issue with my BAXI 105e DHW. if i turn on the hot tap the pump starts and demand for DHW is shown, after a some seconds it...
Replies
1
Views
523
Hi all, thank you so much in advance for any help. I’m always really grateful for the advice and support from experts when I have been on here a...
Replies
2
Views
1K
Hi all I really need some help or advise….. Back story….. Some years ago my dad had an extension to his house which included a newly built...
Replies
2
Views
375
Desperate for some help! Be a life saver of someone can help as suffer from a high intolerance to noise. Moved into new house 1940s (copper...
Replies
7
Views
845
Back
Top