When I have my hot water on and the central heating is off, there is still a small flow of hot water through the motorised valve for the central heating. There's sufficient flow to slightly warm some of the closest radiators. Does this usually mean a new motorised valve or is there something that can be done with the existing valve?

Thanks for looking,

Steve
 
Yes the whole valve needs replacing
 
1. You can get just the valve internals for Honeywell valves. Different for pre 1987 valves (no dimple on the cover) from later valves. However, fitting them is just as much, if not more, work than replacing the whole valve.
2. If the last joint on the return pipe before the boiler isn't the hot water primary (non-combi boilers) you can get spurious circulation through some or all of the radiators.
 
Status
Not open for further replies.

Reply to Honeywell Motorised Valve Not Fully Sealed when Closed in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a plumber coming tomorrow to change a cartridge on a badly dripping tap on my bathroom mixer unit. There is no separate isolating valve for this tap so I'll have to close the stopcock. I tried closing it today but it won't go absolutely 100% closed and there is still a very slight flow...
Replies
1
Views
228
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
226
IS IT POSSIBLE TO ADJUST THIS MIXER UNIT? WE HAVE TO HAVE IT TURNED ALMOST FULLY ANTI CLOCKWISE TO GET HOT WATEROUT. THE FRONT PLATE WITH MIRA ON IT PRISES OFF AND INSIDE THERE ARE SOME PLASTIC BITS AND A SMALL CROSS-HEAD SCREW IN THE MIDDLE. THANKS
Replies
6
Views
219
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
3
Views
354
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
166
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock