My boiler Ideal Logic 30 Combi shows flame loss error (F2 fault).
Boiler is in the newly property and so far has been used just for hot water, which worked fine.
The problem appeared when I tried to switch on central heating (The CH system has been drained, flashed and refilled).With "C" on the screen the blue light appears for 3-5 seconds. The boiler buzzes and then goes off and shows F2.
According to the manual it looks like it's flame detecting electrode fault. But the problem could be with ignition electrode or spark generator and etc.
I would like to order the parts in advance, before my installer arrives, as he is abroad now.
When I checked the boiler (there no leaks inside/outside the boiler, condensing pipe is not blocked and clean, condensing trap is clean and filled with clean water) I've found there a hole in a flame detector electrode's silicone sleeve (on a pic).
Could this be a main problem?
As I see the silicone sleeve and electrode being sold separately everywhere. If this is the problem it would be pretty cheap repair, comparing to more expensive parts like gas valve or PCB (also mentioned as possible reasons for fault F2 in a manual).
Any ideas or advice from the experienced please?
Thanks in advance!

cover_hole_small.jpg
 
Mate, put the cover back on. Phone the manufacturer, if its nearly new, get them out to fix the issue under warranty. Stop touching things that you don't know about. Please just get the thing looked at buy someone who can check it is safe once the cover goes back on.
 
Status
Not open for further replies.

Reply to Ideal Logic Combi Flame Loss problem edited - advice needed in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

W
Hi all, I've got a bit of a strange issue relating to my Ideal Logic Combi 35 which has recently started displaying a F2 error when trying to use...
Replies
2
Views
993
Williams25
W
  • Question
I've got a 2016 Logic PLus Combi 30 and a Salus RT505TX RF Thermostat The thermostat seems to keep losing connection, no matter the placement. It...
Replies
4
Views
786
Hi, As per the thread title, I have an Ideal Logic Combi 30 and I am having a problem with the pump, which keeps activating without any DHW/DCH...
Replies
2
Views
1K
  • Question
Hello guys! I had an Ideal Combi Logic+ C24 fitted in August 2021 in my mid terraced house and I started noticing that it was losing pressure...
Replies
9
Views
1K
Hi. I have an issue with my Ideal Logic+ System S24 boiler which I hope someone can help with. Below is as much detail as I can think of. The...
Replies
4
Views
1K

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock