Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.
  2. Checkout our Plumbers Insurance area - heavily discounted Public Liability Insurance and Van Insurance specifically designed for plumbers.

Discuss ldeal logic + 30kw combi in the Gas Safe Register Forum - Public Forum area at UKPlumbersForums.co.uk.

Tags:
  1. plumber_UK

    plumber_UK New Member

    ideal logic combi losing pressure daily. Initially i thought it was a leak on the system so all the pipework was checked and no leaks found
    The flow and return were isolated overnight with no demand and there was a pressure drop. I disconnected the condensate pipe and put a bucket under it but no leak.
    I did the check a second night but it didn't drop.
    i thought i must have missed something so i have isolated the flow and return again and the pressure has dropped within 30 minutes by around 0.5bar.

    Has anyone come across this before ?

    The boiler is under warranty but i dont want ideal to come out and say its nothing to do with the boiler.
     
  2. sammathias

    sammathias Plumber GSR

    Get ideal out. Tell them.you have isolated the system pipework and pressure has still dropped.
     
  3. townfanjon

    townfanjon Trusted Plumber GSR Top Contributor!!

    Put pressure up to about 2 bar and try it
     
  4. scott_d

    scott_d Plumber GSR

    Any drips from the PRV pipe outside?
     
  5. jtsplumbing

    jtsplumbing Plumber GSR

    Get them out on a warranty call, could have a pin hole in EX , but don't mess around with boiler if still under warranty
     
  6. plumber_UK

    plumber_UK New Member

    Thanks. i'll get ideal out and see what they say.
     
Loading...
Similar Threads - ldeal logic 30kw Forum Date
Flow sensors ideal logic heat only Gas Safe Registered Plumbers Only Aug 24, 2018
Ideal Logic Combi - Low Working Pressure Gas Safe Registered Plumbers Only Aug 2, 2018