Hi,I am doing a large new instalation of a ground source heat pump with underfloor heating to three floors having 7 large manifolds, plus hot water etc.My question is about the hot water side. As I have mentioned this is a large property and it is thought having a electric pumped hot water loop with two 300 litre hot water tanks next to the heat pump and buffer tank is the best method of delivery the hot water to the nine bathrooms, wc's kitchen, utility room etc., But I can't get my mind around thinking how having a permanent pumping of the hot water is not a very green idea and what of the balancing of the hot water pressure with that of the cold water to all the showers etc? I am open to this method but presently my preference is to have three water water tanks in their best positions which can supply all of the water within a suitable distance and keep the water pressure balanced throughout, although saying this there are two water mains to this property. This however I would have thought not present a problem as long as they can both be turned on/off together and with suitable notices and making this aware to the owners and having check valves installed on each main by the stop cocks? The considerable pipe-work loop to the the underfloor heating manifolds which starts with some length of pipe having a 50mm bore then reducing en-route down to 22mm at the furthest distance manifold valves. this loop could be altered to allow heating of the hot water tanks coils with suitable valve controls albeit having higher heat pump water temperature, and thereby also saving much extra pipe work?The other thing is there is a two phase electric supply to the property. One having a 3.84kw of PV panels on one phase and the other having a cheaper off peak supply to mainly the heat pump and hot water tank immersion heater top up for use in the early hours of the morning.I should be glad of any input or thoughts from any interested person?Many thanksMartin
whats your background ? eg big installations (schools hotels etc) if not get a m and e contractor/consultant
Hi Martin,
First thing is to see how you can control the temperature of multiple cylinders via the heat pump controller. That may be an issue depending on what kit you're using.
Sounds like an interesting job.
Are these unvented HW tanks? Also, how does the CoP stack up for getting the higher temps for hot water? I know GSHPs have higher CoP than ASHP but presumably it would go down as the outlet temperature goes up.
As for energy losses by having the cylinders nearer the points of use, depends on how far the circulation goes and how well the pipes are insulated. I've just designed a HW system for a factory which has about 40m run from water heaters to furthest point of use and total heat losses of about 1.5kW. If you've got central hot water with multiple cylinders you've got good recovery and backup. If you spread the cylinders around with each doing a few bathrooms you reduce the HW losses slightly (but lose more on the mains to the cylinders due to higher temps) but lose the redundancy.
Did a 50 room mansion 5 years ago where i was going to put three cylinders around the place, but after the architect and client faffed around with the room layouts there was no space for them and ended up in a central utility cupboard with pumped circulation. Works alright.
When you say pumped do you mean circulated using a bronze pump. If so a well lagged hot water loop might be more cost effective than running off dead legs to get hot water to the furthest bathroom taps?
Hi Guys,
Many thanks for all your advice and questions requiring further information. It is really good to have some dialog with other people who have some experience in such matters because they are really very thin on the ground. Even in my limited experience I have found even the manufacturers and major suppliers of heat pumps and renewables don't always get it right. The first half of this instalation covering half this new property we were told we would only need one circulating pump but soon found this didn't work. Plus where I trained to get my certificate for the installations they even under estimated the size and number of their own bore hole to deliver their own heating needs from a gshp when it iced up majorly in the first year. So I like to not just take their advice without questioning it, because at the end of the day they are mainly there to sell you their products and not always to interested after having made the sale.
To answer some of your questions, Sparkgap and Nostrum, this is a new instalation with new unvented 300 litre hot water tanks. This is my property and so why I want to get it right. It has a distance from the heat pump to the manifolds of approx 50metre run of pipe (100metres including return) The Cop you are correct does reduce quite significantly from 4.2 for underfloor heating down to something like 2.4 for hot water heating. The pipework to have good insulation plus much of the pipe runs are also in an insulated void as well. My view is if it's has a pumped loop the hot water is in the pipes for 24 hours a day so as well as having to pay for the running cost of the pump/pumps there is also the greatest potential heat loss from this system with heat loss wastage getting past the insulation?
You are right Nostrum the biggest hurdle is how to control all these valves to combine the hot water with the underfloor heating if the combined system is to be implemented, and I am open to any advice or input.
Anyone have any views on the balancing of the water pressure with the pumped hot water system? That is another of my worries using the pumped hot water loop system.
Thanks for your time
Regards,
Martin
Re: Pump pressures. You will find the circulating pump will not increase the pressure of the water in the system, it is there to keep a flow of hot water around the ring main.
Generally when a tap is opened, a non-return valve will stop the flow of water through the pump.
Without going into in depth technical reasons - just exclude that from your worries.
Balancing shouldn't be too much of an issue either. I take it that the ring main will be a minimum temp of 65C. You will need tempering valves for each individual bathroom.
With a correct set-up balancing of the water flow through these valves can be achieved relatively easily.
Re: Heatloss through ring main. You will get some heatloss, but it will be minimal, if insulated correctly.
If the pipe is sized correctly, the pump sized correctly, the heatloss will be equivocal to the heatloss from the cylinders.
As for being green and energy efficient, you will only be able to do so much, particularly on a system of that size. But do what you can because it is a saving on money spent on energy.
Out of interest, what is the place for - family home or something else?
Hi Guys,
Regards,
Martin
Hot water circulation and pressure: if you're running an unvented system a circulating pump will make virtually no difference to balanced pressures for showers. Usual unvented pressures are about 20-30m head equivalent while a typical HW circulating pump may generate 0.3-0.6m so any pressure difference is minute. Circulation means you don't have to wait ages running off all the cold water in the pipe before it gets hot and by keeping the hot water circulation temp high enough it helps prevent legionella. Another option used where they don't have circulation or a few long runs of pipe is to have trace heating tape to keep the pipe hot, but that means you are almost using electric to heat your water and still need decent pipe insulation. Either way, unless you've got the heat pump, cylinders and outlets all close together you're going to use electric to shove water around somewhere and this is the best way.
You could go 'old skool' and look at gravity circulation :rofl: which doesn't need a pump but suspect you might lose even more in heat than you save in electric! Besides, modern pumps are pretty skimpy on power consumption. Do you actually need the HW circulating 24/7? Having it only running when people need it would save some money.
When you refer to combining the system and controlling valves etc, I assume you mean making sure the system will cope under design conditions with both? I take it you've got a buffer tank on the GSHP which should provide a reserve for such occasions, just make sure it's sized correctly.
As for sizing GSHP/boreholes etc, I believe the norm is to do a test beforehand to check what sort of flow rate/heat transfer can be taken from a borehole as this is dependent on geology/depth/ground conditions etc. I've mainly dealt with ASHP and the effects of outside temps tend to be more pronounced: I've mentioned elsewhere about a recent installation where the consultants/manufacturers came up with a certain size of unit, but when we queried that their design temps were 7C outside while ours were -3C for full heating output they had to amend the plant size up by about 30% due to the lower output at the lower temp. I have seen some jobs where they have a nice economical heat pump, then slap on several kW of electric heater for when it gets really cold and the heat pump can't cope!
The biggest question is which heat pumps are you proposing as they differe quite fundamentally how they heat hot water and manage the heating of it.
So
1) Whose GSHP's / What spec have you chosen?
2) What's the Heat output at B0/W? What W are you designing for?
3) What's the peak kW demand on the property?
4) What the total kWh/annum from the heat pump?
The answers above will have a MAJOR impact on how the returning secondary (colder) DHW affects the heat pumps.
5) if you're considering running the heat pump(s) on offpeak electrcity, what size buffer tank are you designing?
6) Are you MCS certified?
7) How are you proposing to manage the timing of the heating for the DHW cylinders?
It would be better to run the DHW on a completely separate (set of) circuits direct from the Heatpumps.
Insulate ALL pipes except those specifically designed to emit heat - especially the primaries to and from each of the DHW cylinders.
If you've got 50m from the heat pump to the manifolds - is the heat pump in a separate building?
If so a highly insulated heat main may be the best way to get the flow and return to and from the heatpump.
Wherever it is those runs should be well insulated. 25mm ideally 19mm absolute minimum.
The DHW secondary circulation pipes also need to be insulated
Hi Sparkgap & Worcester,
Many thanks again for for your comments and input, this all very helpful and much appreciated? To answer some of your questions, the heat source for the heat pump is from nearly a 1000metres of underground pipe work in our field and the heat pump is situated in our attached garaging adjoining the house and the existing pipe work is very well insulated with 25mm lagging, and I am MCS certified to install heat pumps, pressurised hot water cylinders etc.
This system has all been designed to accommodate all the domestic output of those living here and with a pumped circulating hot water supply. But I cannot see even though I appreciate the pumps use little electric how pumping hot water around 24 hours a day is better than using well placed hot water tanks? Also thank you Sparkgap for your bit about the pumped water pressure that is good to know and will help me in my decision of which way to go.
i know the pumped hot water is the way all the designers and suppliers have gone down for such wide spread domestic use but I wonder is it because it's the way they always do it, and nobody seems to questions it, and perhaps because it is less complicated to install? But I keep thinking of all that piping hot water being pumped around even in the best insulated pipe work how it must lose a considerable amount of heat. Consider if you would that probably throughout April - November the underfloor heating in any new built house is not required at all because of the high amount of insulation in all the floor, walls and ceiling etc., which now means you need hardly turn any heating and only a little heating even in the winter months, especially when it is as mild as it has been. Then all the pipe work to the U/f/h here shall be standing idle for all these months, when it could be also used in the heating of the hot water tanks by default on this pipe work to come on each night with the cheaper off peak supply to heat the water tanks? By the way there is a 150 litre buffer tank on the run by the heat pump. The emmersions could then come on for say an hour to top up the hot water to bring the tanks up to 65-70 degrees as required and then around 5am if the underfloor heating were calling for heat using a time switch and room controllers the underfloor heating then opens the valves to those manifolds calling for heat to then warm up the house?
Is this a ridiculous cenario I am contemplating which might be too complicated and risky or is this a better more efficient way of utilising one considerable length of pipe work loop instead of two and a more efficient way of saving electricity with 24 hour pumping and the inevitable heat loss this must to some degree cause? That is what I am trying to decide.
Many thanks again for all your help and input.
Kind regards
Martin
What is the heat loss for the property ? 1000m doesn't sound anywhere near enough based on your description so far.
The heat pump is a brilliant solution for a well insulated property
I'm really concerned that you don't know how to design this and you will end up with a system that just won't work
so you
You need to answer my previous questions before anyone give you any more help..
Back of a *** packet calc: typical HWS pump about 20W, therefore running 24/7/365 uses about £27 of electric at 15p/kWh. If you add in 1" insulated pipe for 50m at about 10W/m losing heat from the GSHP at about 4.3p/kWh it loses about £190 worth of heat in that time. Obviously if you only have the HWS circulating for half the time then the costs halve as well.
If you have your cylinders at the other end instead, and only a short run of circulating pipework you lose less from the HWS but more from the mains to the cylinders (in this case because of the higher primary temp the losses would go up 50% for the same size pipe) plus you'd need a more powerful primary pump=higher running costs, so you'd probably save very little if anything.
Kind regards
Martin
From the sound of it then you're looking at using the heating mains around the house to feed the cylinders and manifolds and zoning using local motorised valves. Fine, just means the mains have to be sized for the increased load but perfectly acceptable. If you're also using the immersion heaters to top up the hot water (I take it the GSHP gets it up to about 50-55C and the immersion does the rest) then that would add to the running costs if you had long runs of circulating pipework.
Pumped HWS is usual in commercial installations and larger domestic ones where you usually have all the plant in a central plantroom or aren't able to have cylinders near to the main points of use. Also, if you've got sinks or whatever scattered around the building you need circulation unless you are willing to accept lots of water wastage drawing off cold water from long dead legs.
All that's good there are still fundamental issues with Martinplumber's designs though - for example Heatpumps work on a 3 port diverter valve, so where will he put the buffer tank, how / why would you share the flow/return with the 7 heating manifolds.
This is a very straightforward system, being made complicated by the OP, who seems to lack fundamental understanding of heat pumps and plumbing systems and building regulations and MCS requirements and says this is for his own house, and the VERY worrying thing is that he is MCS certified ..
7 LARGE Heating manifolds 3 x 300 litre DHW cylinders, unless this is a passiv haus, (or close to it ) then 1000m can't be any near adequate, unless he got hot rocks... Round here it works out in the order of 100m/kW so that's only 10kW ....
Hi Sparkgap,
Many thanks for your help and information which has been very helpful in helping me decide to go with the pumped hot water loop method as was designed. Your figures even off the back of the *** packet are very helpful, combined with the limited pressure loss information of yesterday within the pumping loop has finally sold me on sticking to the method as was designed for the remainder of the system.
Worcester, I do find some of your comments very rude and lacking in respect for your fellow plumbers especially when you know so little of the facts. I didn't know you were going to inspect every avenue of my gshp system, as I was only enquiring whether there was a need to have a circulating pump for the hot water over this distance. You might like to know I am in fact already using the same system as sought with a three port diverter valve and buffer tank installed but to a smaller scale yet still without pumping the hot water whilst heating just 3 manifolds of ufh, the hot water plus three large heat exchangers to a swimming pool in the summer months. The 1000metres of pipe mentioned are coiled slinkies so it's total length of pipe run are nearer to 4000 metres and of a larger bore pipe than from some suppliers, laid flat within 2 acres of south facing land. Plus this gshp system which has cost me over £150,000 is not being installed by a half wit and as I have said has been calculated by professionals who I am happy to take the their figures for the length of slinkies as being adequate for this property. And yes I am MCS approved but nevertheless always willing to learn and never thought I knew it all like some people it seems. Admittedly what I have sought is probably more to do with an electrician than a plumber but nevertheless joined this forum to find out if there was anyone having experience of installing a system over such a distance and in such a way as using two phases of electricity to the best advantage, which obviously you haven't. Your comments are very condescending, disrespectful and do spoil the good work some people who simply write to help others within this forum.
Thank you once again for your help Sparkplug which is very much appreciated.
Kind regards
Martin
It was simply that you consistently didn't answer my questions..
Indeed whilst trying to help you not make a very expensive mistake, you completely disregarded them and wouldn't give any facts.
-ends-outahere-
Hi Worcester,
Sorry was having a bad day and a bit touchy. in fact I have since checked and its 6600 metres of underground slinkies we have, so should be enough for the domestic side.
Have a good day and apologies again.
regards
Martin
Martin,
Depending upon which heat pump(s) you are using, how they are configured, how the three DHW tanks call for hot water and how the heat pumps are configured to deliver that is critical.
A 150 litre buffer isn't going to be able to supply heat to a house with 7 ufh manifolds for very long at all lwe are talking of only minutes of heat storage there, and there is a danger that the heat pumps are never able to provide heat to the house.
If you are confident that your installer has got all that covered then fine. - It was my concern for you in that area that has been prompting my questions to you.
There is a big difference between 1000 and 6600 meters :)
why don't you fit a stat and a timer to the secondary return no point keeping it on 24/7