commercial kitchen has an old burner with no FSDs, presently its possible to turn the gas on and walk away without lighting it

needs a new piperun with an interlock,
obviously its advisable but does it also have a low pressure cut off or some sort of pressure proving device

cant recall whats the legal minimum was

one of the chiefs must have lent on the oven control knob while cleaning, filled the oven with gas which subsequently went bang and blow the doors open when she lighted the hob
 
Last edited:
Yes! Low pressure sensor with interlock to solenoid valve and interlock with ventilation extraction system is what you need. Similar scenario to chemistry labs in educational establishments.
 
thanks Reg,
I knew about the extract just couldnt remember if the low pressure sensor was mandatory
 
Status
Not open for further replies.

Reply to no FSDs in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Non-professional / knowledgeable person here. I'm a Brit in Romania who volunteers for a charity building an old peoples home for needy old people. Out here competence and integrity is harder to come by in a worker, in fact it's hard to find workers at all where we are in the countryside...
Replies
3
Views
373
Hi all, I'm going to be getting my cookers ticket soon and I'm a little confused on the classification for faults. If I turn a gas oven on and its starts on high flame what would this be classed as? Also for things such as fsds on hob burners I am assuming that if it doesnt keep the burner lit...
Replies
2
Views
74
Condensing boiler installed by local Gas Safe plumber in 2014, not combi. Failed a couple of weeks ago with flashing blue light which googling suggests means no gas, blocked flue or blocked condensate pipe. There is gas, the flue is clear, and the condensate pipe goes into the under-sink waste...
Replies
7
Views
4K
In our Village Hall we have a Ideal Concord CXS/SD40/H central heating boiler. This was installed new when we had an extension built and the existing boiler needed upgrading. The Mechanical Engineers advising the architect insisted that we had a conventional cast iron combustion chamber boiler...
Replies
10
Views
1K
New LPG installation with 2x 19kg cylinders outside, plus change-over regulator with isolator valve on output, then 10 metres of 15mm copper pipe (3 soldered joints only) running into house to the kitchen, to gas hob (with another isolator just prior to hob). System Failing tightness test...
Replies
9
Views
2K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock