mfgs

Plumbers Arms member
Plumber
Gas Engineer
Messages
3,470
I am having a bit of a nightmare with a Profile 100e. I was called in because it was over heating and kept tripping them stat. A new pump was fitted about 6 months ago. I put my clamps on the flow and return pipes directly above the boiler and the overheat stat was tripping when the flow pipe was at 72-75 degrees, spoke to technical who said it should trip at 95 and to replace the stat. New stat fitted and exactly the same issue.

Then my customer informs me that another plumber was here before and spotted the pump was on the wrong way round and had flipped it. When I checked it, it all seemed fine, pointing away from the boiler and towards to two zone valves. Then I went to check the f and e tank and the cylinder. Feed and vent come off the flow and return to the cylinder like an old gravity set up.

So back to the boiler and a quick look in the manual shows the pipe the pump is on should actually be the return ( the manual shows the flow being the left hand pipe on the boiler and the return the right) but the pump is pumping away from the boiler. The main boiler stat is situated on what should be the flow pipe but with the current set up is now the return. So is it acceptable to swap the pump around to the way it was previously pointing back to the boiler, with the zone valves essentially behind it? Can you zone on the return like that? There is a manual bypass fitted as well.

Sorry for the long post, this one just has me a little confused.
 
Last edited:
Also just to point out, the boiler was suffering from the over heating problem with the pump facing both ways. So swapping it around may not cure it but hopefully it will help point me in the right direction and give me the ability to check the boiler stat more accurately etc.
 
When is it overheating? On shut down when the valves shut? Maybe the pump overrun has stopped working?
 
That's even if there's a pump overrun wired in. Don't these have a pumped and gravity switch on the front panel?
Surely the stat has failed if it's getting that hot? The stat should be clicking off on temperature well before 95!
And it should be fine swapping the pump back, it would put the f and e pipe in a better position with regard to the pump.
 
Last edited:
It overheats when the pump is still running. The boiler stat isnt shutting it down as currently its on what effectively is now the return and I have about a 13 degree temp difference. The pump is wired in to the boiler, but it overheats before the boiler stat is kicking in.

I'm thinking of swapping the boiler stat and switching the pump around?
 
It overheats when the pump is still running. The boiler stat isnt shutting it down as currently its on what effectively is now the return and I have about a 13 degree temp difference. The pump is wired in to the boiler, but it overheats before the boiler stat is kicking in.

I'm thinking of swapping the boiler stat and switching the pump around?

That's your problem then, it needs to be reading the flow.
 
Yeah agreed, but my customer has told me this issue was still happening before the pump was swapped around. So think there must be a secondary problem.
 
At least the customers aware, so no daft arguments over the fix.
 
Yeah agreed, but my customer has told me this issue was still happening before the pump was swapped around. So think there must be a secondary problem.

If I'm right, the issue existed before the other plumber swapped pump around.
( he was wrong of course). You swapped the overheat but the pump is now pumping the wrong way so the boiler stat/flow sensor is reading the return.

If you put the pump back to how it should be, you may find that the problem is solved !

If not, it's not really your fault that his antics threw you !
So start again after you've explained to the customer.
Ask if there is anything else you might need to know

and whilst you're at it, put those MV's on the right pipe
 
I don't think the over heat stat was the issue as its tripping at exactly the same temps as before. Until I get back and swap the pump around I don't really know where I stand.
I love and hate jobs like this, I enjoy a challenge but this is just annoying me as I am struggling for time to fit it in. Every time I speak to the customer he gives more info, turns out I am actually the third person to have a look at it. I was originally called because the heating wouldn't come on, swapped the actuator, got that working and then he mentioned this.
 
I'd be looking a re-piping as per MI's, theres an estate near me which has Ideal Classics, all open vents and piped wrongly, if they start drawing air in its usually game over until its piped correctly. Just thinking your fault may not lie with the boiler if the OH stat has been ruled out
 
Can you trace pipework from boiler to cold feed/vent, cylnder coil, pump and zone valves etc. If you can you can determine if it's piped correctly. I came I cross loads of fully pumped open vent systems which are piped incorrectly and must have been drawing in air since day 1. If I can't trace all pipework or looks like it's wrong I generally seal the system, expansion vessel, filling loop and PRV. Dump the header tank and cap open ends. If it's air that's causing the issue job done!
 
Repipe it the way it should have been done and be prepared for sludged up sections that won't flush and will need replacing .Be sure to cover yourself well with pricing
 
Status
Not open for further replies.

Reply to Potterton profile 100e in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Firstly I won't be touching or going anything... I only want advice if this is right.. my partners dad has a aga that is solid fuel unregulated heat source and a oil boiler. The problem the hit water cylinder doesn't have a stat thus why the hot water is roasting hot but there is a pipe stat on...
Replies
3
Views
349
    • Like
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The existing pump flows downwards. The manual for the proposed replacement recommends that it should pump upwards. This would involve rearranging the flow &...
Replies
8
Views
606
R
Hi, The outlet of all my radiators are at 55°C, but the boiler keep showing the Return Temperature is 60°C (and keep raising at 1°C/min rate) Also the flow temperature keeps going up above the set point and when it reaches +5°C above the set point, the boiler shuts down (even before the room...
Replies
0
Views
198
Renato
R
C
I’ve had an Ideal Vogue 32max/gen2 system boiler to a Megaflo fitted a week and running it at Flow temp 73 degrees to getting a return temp of about 55 degrees C, I’m seeing the LCD screen saying the efficiency level is only 25-28%. Has anyone else seen such a low percentage? I know for a fact...
Replies
2
Views
337
I would like to add an additional radiator to our central heating system. We have an attached double garage converted to a man-cave and workshop (with dividing stud partition wall) currently not covered by the central heating. The former is not currently user friendly in winter, and we get by...
Replies
5
Views
518
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock