Hi to all,

I have bought a new radiator as replacement for old one.


After installation by plumber, the new radiator is heating up only to 1/3 of high. The rest remain cold.
Also, radiator is making quite loud noise when heating up.

The system/radiator is free of air.

My plumber was wondering if it may be a directional type of radiator, but he could not find any additional info in manual or any labels or arrows on radiator itself.

It looks like it it vertical type that can be installed horizontally.

Any suggestion, what can be a problem please?

Maybe someone from forum have already installed this model?


I am not a plumber, by my thoughts are it may be a wrong connection or baffle?

Any suggestion really appreciated.
 

Attachments

  • 617O+FBXskS._AC_SL1000_.jpg
    617O+FBXskS._AC_SL1000_.jpg
    100.7 KB · Views: 26
did it come with the bleed / seal nut fitted, if not has it been hung upside down,
i"ve only fitted 4 of these and they have had stickers on saying in, out,
 
Please find photos attached.

There is a baffle in one of the photos.
 

Attachments

  • 20231103_093625.jpg
    20231103_093625.jpg
    342.5 KB · Views: 16
  • 20231103_093513.jpg
    20231103_093513.jpg
    553.9 KB · Views: 18
  • 20231103_093504.jpg
    20231103_093504.jpg
    363.6 KB · Views: 17
  • 20231103_093441.jpg
    20231103_093441.jpg
    290.4 KB · Views: 20
  • 20231103_093425.jpg
    20231103_093425.jpg
    460.1 KB · Views: 17
  • 20231103_093418.jpg
    20231103_093418.jpg
    476.4 KB · Views: 18
  • 20231103_093411.jpg
    20231103_093411.jpg
    468.3 KB · Views: 18
have you followed instructions on page two?
have you got the flow going in at the correct side of the rad.
 
as far as i know, no. got to be the right way,
did you follow instructions on page two?

got to go out work rang
 
You might the look of that, but it has no fins. The claimed output is 6557 BTU but at T60. A mean radiator temp of 80 degrees is crazy hot.

Installed on a new system, designed to regs for flow of 55deg return of 35deg, this radiator would put out 2255BTU, or .66 kW.

B2-EN442 states all hydronic radiator and towel rail outputs are tested and presented at Delta T 50° or ΔT 50°. So an illegal advert in Amazon.
 
You might the look of that, but it has no fins. The claimed output is 6557 BTU but at T60. A mean radiator temp of 80 degrees is crazy hot.

Installed on a new system, designed to regs for flow of 55deg return of 35deg, this radiator would put out 2255BTU, or .66 kW.

B2-EN442 states all hydronic radiator and towel rail outputs are tested and presented at Delta T 50° or ΔT 50°. So an illegal advert in Amazon.
What does it mean for " no plumber" please?
 
as far as i know, no. got to be the right way,
did you follow instructions on page two?

got to go out work rang
Think he is trying to say that if horizontal you have to remove the blank that will be in the end pipe as it won’t flow it is there for when it’s vertical to assist the flow up to the top and carry on with its convection. Look at page 2 to confirm
 
We had a job where the customer had a similar issue. In the end we just knocked the baffle out with a length of threaded bar and hey presto they worked perfectly! I think the baffle is there for vertical fit to direct the water round.
 

Reply to Radiator is heating up only to 1/3 of high in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
122
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
286
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
439
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
110
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
321