Hey all,
Been out to one of these this eve and practically stripped it to bits but could not get it working.
Basically, when there is a demand for CH the flow switch is not being activated. The pump runs and I can push the microswitch tab up which makes it fire up but the pin on the div valve is not actuating.
Another engineer has been out and replaced PCB, APS and also a new diaphram on the flow switch (no idea why PCB and APS where changed).
There is some dirt in the system, but nothing major and I've seen far worse. The Fault finding section states the Flow Valve rod is obstructed.
I've no idea where this Flow valve rod is located as it's not in any diagrams in the manual and I was running out of time to keep hunting for it.
So, how do I get to this part or should I just just put a new div valve on?
Is there anything else that would stop the flow switch from actuating?
I'm knackered, my head has gone to mush and I've missed most of the footy 🙂
Cheers
Been out to one of these this eve and practically stripped it to bits but could not get it working.
Basically, when there is a demand for CH the flow switch is not being activated. The pump runs and I can push the microswitch tab up which makes it fire up but the pin on the div valve is not actuating.
Another engineer has been out and replaced PCB, APS and also a new diaphram on the flow switch (no idea why PCB and APS where changed).
There is some dirt in the system, but nothing major and I've seen far worse. The Fault finding section states the Flow Valve rod is obstructed.
I've no idea where this Flow valve rod is located as it's not in any diagrams in the manual and I was running out of time to keep hunting for it.
So, how do I get to this part or should I just just put a new div valve on?
Is there anything else that would stop the flow switch from actuating?
I'm knackered, my head has gone to mush and I've missed most of the footy 🙂
Cheers