I have a Glowworm Energysaver Combi 2 that seems to run all the time even when the heating or hot water are not being called for. Any ideas please? Thanks Mark
 
Have you got the heating turned off via the clock/roomstat, and not the boiler stat just turned zero,

Are any hw taps drippng fast??,

If the pump is constantly run, which of the pipes of the boiler are warm/hot?
 
sentral heating sensor faulty sounds like its trying to disperse the heat, check resistance on thermistors should be around 14700 ohms at 20 degress
 