Gas Engineers > What is the correct procedure attending a boiler breakdown?
View the thread, titled "Gas Engineers > What is the correct procedure attending a boiler breakdown?" which is posted in Boiler Advice Forum on UK Plumbers Forums.
Hi there guys i know this might sound like a silly question. I am a new learner (not qualified yet) and i just want to know the correct procedures on what you should do in an event of a boiler breakdown. For example lets say if the boiler is leaking... Do you Isolate water and gas to the boiler first? or do you have to do the usual let by and tightness test and then the other stuff?
@Scott_1979 @Riley thanks for the reply guys but lets say once you have have fixed the issue with the boiler. do you have to do all of the testing again like...
let by, stabilisation and tightness test?
gas rate?
Working pressures?
Co2 combustion checks?
if you get what i mean?
depends what the fault was
lets say diverter leaking
i wouldnt do a
let by or tt
gas rate
working pressure
or fga test
i would do a visual check of the boiler
visual check of the case seals
and i would listen to how it starts up you can normally guess how its running
1 rule I’ve always followed is
Anything I do with out removing the combustion chamber it’s a visual only.
For example changing a Baxi 105e pump visual only not disturbed anything affecting combustion. Documented well because no one will help you when your standing in the doc. That piece of paper can be your get out of jail card.
If I was changing a pump on a Worcester 24i junior greenstar I’d do a gas rate and record flue analyser readings. Again documented well.
Only do a full tightness test when necessary. If you do a tightness test on every job you’re opening a can of worms.
BG started doing a tightness test on every job but scrapped it soon after.
Homeserve used to do a mini tightness test on the gas valve they scrapped that pretty quickly. (Only do it when changing a gas valve or see if it’s opening)
According to the old regs after a tightness test we had to purge and relight each appliance thankfully now it’s changed. Only purge and relight once you’ve let air in to the system from the furthest appliance away.
There is one important issue here which sometimes gets forgotten. Go through with the customer what is wrong in their words AND then EXAMINE all the rest of the system as much as possible check for other unreported defects. Unscrupulous customers can try and load pre existing problems they know about on to naive fitters. Like you fix a diverter then find afterwards the timer is LALA but they will leave it with you. Generally people are nice and honest but some ...usually well healed ones
Can try it on, ones from Formby where I live are the worst ever for this In my opinion
Regarding Gas, for me, follow the ignition sequence to see where it fails. For more complex problems do all the basics. Pressure, Gas rate, measure voltages and resistances. Never be afraid to call the manufacturers Technical helpdesk, they know their boiler.
So you give an appliance a service after you replace a water part for free
In the real world no one does anything more than a visual
Unless theve changed something that would effect them
Who mentioned a service? You are REQUIRED to conduct the tests outlined in 26.9 whenever you work on a gas appliance. Or does repairing/replacing a diverter valve not count as working in a boiler?
Which is what a basic service is
Fga gas rate etc
(9) Where a person performs work on a gas appliance he shall immediately thereafter examine—
(a)​
the effectiveness of any flue;​
(b)​
the supply of combustion air;​
(c)
its operating pressure or heat input or, where necessary, both;
(d)​
its operation so as to ensure its safe functioning,​
Jeez. You may call that a service. You have no idea to what I am referring, do you?
Yes 26.9 Reference is
Flue gases
Combustion air
Op pressure / input
Operation
Which in turn is the same as you would do in servicing
Shaun. 26.9 is NOT a service. It is the minimum required when attending a gas appliance. Even if you are there to top up an EV, your attention and subsequent leaving it working counts as an affirmation that all is safe with the boiler. The regs demand that, to be sure, you complete 26.9.
Really, what bit do you not understand?
Think you should email bg then
How's the homeowner supposed to do these checks when they replace a diverter valve on a 105
Come on, Shaun, stop digging holes. A homeowner is not subject to 26.9, but, as a RGI, presumably, you are.
Why not same situation also you haven't addressed anything in regards to bg
Also sparkys wiring boiler same checks must be applied then as theve disturbed the seal
Homeowners are not trained as RGI's therefore not subject to the same rules,or have the same responsibilities. In the same way that a removal man can disconnect a plug in cooker without being subject to the regs, whereas we would be.
What about BG? Their RGI's are subject to 26.9. Whether an individual complies is another thing - you clearly do not. I did a short stint as a BG contractor, and their "service", includes all of 26.9.
Re electricians. They should not be removing the case and breaking the seal, unless a RGI is also in attendance to reinstate the appliance. Apart from electricians who also hold gas certs.
Can you not see that the regs insist that you do 26.9. I am a little confused that you are arguing on this. I suspect that any GS inspector reading this would be interested in your ID.
This is from an inspector
Unless your changing a gas part that could effect the burning / you something you need to set it up visual only
Carry on how you are and I will do the same
Fair enough we can agree to do that. But your inspector is wrong, or you misunderstood him. Get him to put it in writing. As I posted earlier, this is a direct lift from the regs:
(a)
(b)
(c)
(d)
I do not see any bit saying this only applies when fitting parts. Are you sure he was not referring tp the need or otherwise of conducting a FGA?
EDIT: For some reason, copying this is affecting the text set up.
Reply to the thread, titled "Gas Engineers > What is the correct procedure attending a boiler breakdown?" which is posted in Boiler Advice Forum on Plumbers Forums.
Ibraheem,
dan_the_plumber,
