Changed 5 radiators yesterday. now customer saying no hot water. 2 2 port valves. hw cylinder in the loft.

Turned hw on at programmer and hear the motorised valve and boiler fires up and is running but for some reason not getting hot water.

What should i be checking? I have to go back tonight

thanks
 
Hi guys

Changed 5 radiators yesterday. now customer saying no hot water. 2 2 port valves. hw cylinder in the loft.

Turned hw on at programmer and hear the motorised valve and boiler fires up and is running but for some reason not getting hot water.

What should i be checking? I have to go back tonight

thanks

Air mate
 
Check for air at cylinder. Look for an bleed vent or crack the flow cylinder Union to let the air escape. Make sure pump is free of air too.
 
Turn the pump upside down and vent the system everywhere possible with it running and boiler stat on low (providing it hasn't got a flow sensor like a solo he) then put the pump back usually does the trick
 
Thanks guys.

It was air as you all said, missed a vent yesterday on a fitting covered by insulation and taped up. Doh! bled the air and felt the pipes get red hot instantly. Sorted.
 