First off I'm not a gas engineer but a fire engineer. I've just had a bit of a problem on a job where the main incoming solenoid valve had been left off but the heaters on the site where then turned on or well where tried to be. They called in a Gas company who found the problem.
But they are now saying that the hole system needs purging with nitrogen as there will be air in the system. Is this correct as I cant understand how air has got into the system? Surely the heaters/burners would just shut of if the pressure was to low and wouldn't let air into the system.

Any advice would be appreciated thanks.
 
wont need purging with nitrogen unless they need to work on it

but depending on volume yes it might need to be purged but not with nitrogen

no they would try and fire till they locked out (eg fault)

where are you located just for reference?
 
Thanks for the reply.
That was my thoughts don't understand the nitrogen bit, I can understand the possible purging with gas bit and also pressure testing after.
Its a big pipe around 12-18 inch and over 150+ meter long so will be a fair volume.
Its around the Birmingham area.
 
Thanks for the reply.
That was my thoughts don't understand the nitrogen bit, I can understand the possible purging with gas bit and also pressure testing after.
Its a big pipe around 12-18 inch and over 150+ meter long so will be a fair volume.
Its around the Birmingham area.

yep air to gas purging unless there working on it doesnt matter on size they will have to be commercially gas safe to up1 spec

whats it supplying just air heaters?
 
Yeah just air heaters all of which have a auto cut off from the fire alarm themselves sadly the main valve relay had a issue and remain closed.
I will recommend to the customer to ask why the company are saying it needs purging with nitrogen and tell them to possibly get a second opinion. Thanks again.
 
Yeah just air heaters all of which have a auto cut off from the fire alarm themselves sadly the main valve relay had a issue and remain closed.
I will recommend to the customer to ask why the company are saying it needs purging with nitrogen and tell them to possibly get a second opinion. Thanks again.

yea best option if you dont mind me asking wheres the cutomer located / site location

manchester ?
 
No I am based in the Manchester area but this site is in Coventry we look after a number of there sites most of which are in the north west area.
 
No I am based in the Manchester area but this site is in Coventry we look after a number of there sites most of which are in the north west area.

Nice little patch

Any other questions/ updates just post away :)
 
The gas pipework will only need purging with nitrogen if work needs doing on the system ie decommissioning like changing the solenoid valve. If its a power failure and the heating was switched on then it will need testing and then air to gas purging and recommissioning. Cheers kop
 
Just a quick up date, the gas company carried out a air to gas purge although I still don't get how air would as got into the system, I would have though the valves would just shut once the pressure dropped.
Anyway it took the gas company about 5 hours for 2 men, think there is 8 heaters in total and a few need a cheery picker to get up to them. Although I think the building owners supplied that. The bill came to around £2.5k in total which I thought was crazy.
 
Just a quick up date, the gas company carried out a air to gas purge although I still don't get how air would as got into the system, I would have though the valves would just shut once the pressure dropped.
Anyway it took the gas company about 5 hours for 2 men, think there is 8 heaters in total and a few need a cheery picker to get up to them. Although I think the building owners supplied that. The bill came to around £2.5k in total which I thought was crazy.

yep sounds about right
 
I still don't get how air would as got into the system

It's more a case of the system having lost pressure.
Safety !
In a large Gas installation you need to be certain that there is no Gas air mixture within. The larger the installation the greater the risk.

If the installation has depressurised for any reason, it should be tested, purged and recommissioned.

This does not mean that air definitely entered the pipe work. It means it is unknown whether it did or didn't and therefore we should treat it as if it did.

hope this makes sense!
 
Last edited:
Status
Not open for further replies.

Reply to Does it need purging? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
319
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock