Discuss 2 Port Zone Valve - Clicking in the Plumbing Zone area at PlumbersForums.net

Messages
3
Hi,

Replaced a dead syncron motor in a Grasslin 2 port zone valve, however when connected back up & triggered by the thermostat it's now creating a constant clicking noise - caused by the actuator lever attempting to move towards the manual/open end.

See this YouTube link for an example of the problem...


Does anyone have any experience of a similar problem or how to resolve? Is it likely the whole Actuator/Valve needs replacing? (Opens up fine if I put it in the manual open position, but doing that doesn't make the micro-switch trigger the underfloor heating pump)
 
You've either not put the motor in properly or the head mech is completely knackered. If so the head will need replacing, however if the back is stiff to turn once the head is removed this could be the cause of the issue. However seeming it's UFH the head has probably been open long periods of time and worn out due to usage.
 
I had a similar problem about 18 months ago & the plumber supplied & fitted a replacement valve for about £200... just a tad annoying to shell out £200 every 18 months for something that I thought I may be able to fix myself as I'm fine with electrics (not knowledgeable enough to replace complete valve myself though)

I will try removing the syncron motor again & reseating it, but as a next step would you suggest getting a replacement actuator or when you say the head may need replacing does that mean the whole valve likely needs to be swapped out? (in which case I'll likely get on the phone to the plumber!)

I don't suppose anyone knows if a Grasslin actuator can be swapped for a Corgi/Honeywell model as they look the same?

Tempted by the Drayton valves as I see the actuators can be swapped out with a 'snap on' installation, so if this is going to be a regular thing it may make replacing easier/cheaper in the long term?
 
Has he not replaced with a Honeywell valve? Honeywell ones are usually pretty good and will last. Not overly keen on the Drayton valves as had issues with the microswitches sticking. At the end of the day it's only two screws which hold the head to the body anyway.

Any valves if they are open for long periods of time won't last, zone valves are designed to be operated 24/7 and hence will burn out/fail quicker if they are used like that.
 
I have a siemens zone valve with a sfa71u 24v actuator. It clicks and sticks at a point, and i have to replace the actuator. is there any other actuator i can use without changing the valve.
 

Reply to 2 Port Zone Valve - Clicking in the Plumbing Zone area at PlumbersForums.net

Similar plumbing topics

Is there anyway of testing electrically with a multimeter or any other way. Of testing that when you turn a room stat up it is creating a demand...
Replies
7
Views
552
I have an older gas boiler HW heating system with a taco circulator pump for each zone that worked fine last season. When turning it on for the...
Replies
4
Views
484
J
Hi I have a honeywell programmer which does 10 min cycles but with the zone valve fitted it is closed during a 4.5 min long pump only cycle. Is...
Replies
3
Views
655
Is there any advice on using Honeywell Evohome with 2 zone heating. Honeywell support are pretty useless and give conflicting advice. They...
Replies
14
Views
2K
Hi all I have been noticing that my gas bills have been excessively high even in the current climate …I did a little investigating and found my...
Replies
6
Views
759
Back
Top