Search the forum,

Discuss Anyone any idea why FGT is 252c in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Messages
12
hi all, came across this today upon doing a service. Everything on o2,c02 was correct, pressure and air correct. New nozzle and correct size but Reading 252c on fgt. anyone any idea what could cause this? I usually aim for around 190-220. It is a 16 year old bluebird

Thanks
 
Hi best,

I used the hole that has been drilled near bottom centre of the flue near were it meets the boiler.

I assume you mean a hole drilled in the actual flue?
I just was checking that, because was thinking you maybe were using the cleaning door test point, which would be too hot.
Ideally on a standard efficiency oil boiler the flue test hole should be away from top of boiler a little - 300mm if possible in my opinion.
Are the boiler baffles in good condition plus staggered properly and shell clean?
If all correct then your nozzle maybe faulty, or nozzle has got mixed up and wrong labelled nozzle container. Seen new nozzles faulty putting out too much oil.
Maybe just check oil pressure with a different gauge to be sure your oil gauge was reading ok.
 
I assume you mean a hole drilled in the actual flue?
I just was checking that, because was thinking you maybe were using the cleaning door test point, which would be too hot.
Ideally on a standard efficiency oil boiler the flue test hole should be away from top of boiler a little - 300mm if possible in my opinion.
Are the boiler baffles in good condition plus staggered properly and shell clean?
If all correct then your nozzle maybe faulty


Yes there was a hole from previous services. All is in good order internally and baffles back in correct order. I might pop back tomorrow and try another nozzle, the flue is the old type with enamel coating on bottom half
Thank you for your reply
 
I edited my above post and added a couple of points to check
 
Yes there was a hole from previous services. All is in good order internally and baffles back in correct order. I might pop back tomorrow and try another nozzle, the flue is the old type with enamel coating on bottom half
Thank you for your reply

Doesn’t happen often, but sometimes a faulty brand new nozzle causes bother.
I saw a 120 Warmflow Bluebird that was burning serious and put pure bitumin coating (literally) on inner shell. Turned out it was the service idiot had just prior to this, put a new nozzle - a 0.5 instead of a 1.0 gallon Danfoss nozzle. Was seriously overaired
 
Doesn’t happen often, but sometimes a faulty brand new nozzle causes bother.
I saw a 120 Warmflow Bluebird that was burning serious and put pure bitumin coating (literally) on inner shell. Turned out it was the service idiot had just prior to this, put a new nozzle - a 0.5 instead of a 1.0 gallon Danfoss nozzle. Was seriously overaired

Would that kind of temperature be a real drama?
 
Would that kind of temperature be a real drama?

Maybe not on your boiler.
I forgot to ask you what output of boiler it was?
I find the Warmflows of that vintage had tight baffles that get easily damaged if severe heated and although if lots of sulphur blocks around the baffles it obviously results in them being over heated, it also happens to fairly clean ones
 
Maybe not on your boiler.
I forgot to ask you what output of boiler it was?
I find the Warmflows of that vintage had tight baffles that get easily damaged if severe heated and although if lots of sulphur blocks around the baffles it obviously results in them being over heated, it also happens to fairly clean ones

I think it was 26.4kw output
 
An example of real overheat was on a 50/70 bluebird I went to service and discovered NO baffles. The oil pressure had been accidentally raised by the tenant to I think near full gauge pressure . But it had been left like that for a long time.
The two baffles had just nearly disappeared, with just fragile thin pieces of metal in boiler base.
Must have cost some kerosine :p
 
An example of real overheat was on a 50/70 bluebird I went to service and discovered NO baffles. The oil pressure had been accidentally raised by the tenant to I think near full gauge pressure . But it had been left like that for a long time.
The two baffles had just nearly disappeared, with just fragile thin pieces of metal in boiler base.
Must have cost some kerosine :p


At least they were heating the atmosphere :)
 
Status
Not open for further replies.

Reply to Anyone any idea why FGT is 252c in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi guys....we have an old Astracast sink top....I think its a composite sink....has a big single bowl. My wife thinks it looks scruffy....looks ok to me.....sound but the bowl has seen a lot of work. So she wants a new one...Astracast it seems are no more. The problem is its size.....looked...
Replies
2
Views
160
Hi all, I'm installing a concrete patio out back. By the wall under the kitchen sink I have an existing P-Trap gully for the grey water from the sink, dishwasher, washing machine etc. When I pour the concrete there won't be any chance to dig it up anymore. From my own research I get the...
Replies
0
Views
139
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
362
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
222
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
261
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock