Hoping that someone might be able to help me.

I have a sealed heating system comprising 15 radiators and hot water cylinder. In the last 18 months all radiators were replaced and plumbed using 10mm microbore pipe back to manifolds on 22mm flow and return pipes. The system is S plan with two heating zones and hot water.

The problem I am having is that the auto bypass lets hot water through in any combination. When both upstairs and downstairs heating is on the boiler stays on and good heat is achieved, although bypassing. When upstairs is on in isolation the bypass is open and the boiler starts short cycling and also does the same with hot water only.

Initially I was concerned that the microbore pipe was causing too much resistance of flow which was resulting in the auto bypass opening. However, the bypass also opens for hot water only which is not in small bore pipe so makes me think it is not this.

I have had the auto bypass replaced, so it is not a faulty valve.

The pump was re-used from the old system and is a 15/50, I wonder if this is not man enough to overcome the resistance of the new small diameter pipes? But this would not explain the bypass being open for hot water only?

My other line of thinking is that the heat exchanger may be clogged up causing a restriction, we are in a hard water area and had a period where the boiler was kettling last year.

Overall the heating and hot water work, but not as well or efficiently as I believe they could. Really I'd like to find a heating engineer in Norfolk who really knows their stuff, a couple of people local to me have been round and I've been advised to change the boiler which I just don't believe.
 
If I am looking at your boilers M.Is then 4.3 - "a variable duty pump should be set to give a temp diff of no greater than 20deg C"
"Important F&R pipe sizes - up to 18kw = 22mm, >18kw =28mm"
The flow rate required to provide 18kw @ 20 degC would main that your pump would loose approx 1M head just pushing that amount of water through the heat exchanger if you needed it full 30kw you would loose over 2.5Metres.

Your existing pump is a 5M head but that is the max it can push with no or little flow. Moving approx 0.215L/S it would only develop a pressure of approx 3.7M head, less the boiler 1M, would leave approx 2.4 M for the rest of the system. Not likely to be enough to overcome the resistance you have put in by re-piping in 10mm.
 
Fit a Grundfos pump with proportional pressure function? God knows, that's why I'm asking! Someone else must have come across this before?
Yes Chris thats why they were invented.
If you fit one would you need a by-pass ??
I don't think you do & have had my one at home closed for couple of years now with an Alpha 2 installed.
But if you do want to provide the minimum flow then why not use close coupled tees instead of LLH (to expensive) to provide hydraulic seperation. You are going to buy a new pump anyway so give it a go!!
 
Thanks, makes sense to me. Although is 3.5m head sufficient for the longest microbore to manifold circuit of 18m? My rough calculations would suggest not.
It's not just the length of the pipe which is important. You have to take into account the flow rate, which depends on the size of radiator and the temperature differential. For example:

Resistance of 18m of 10mm pipe connected to a 2kW rad with a 20C differential is approx 0.58m, with a 10C differential it is approx 1.94m. The flow rate has doubled so the resistance increases by four times.

Upload your rough calculations and I can take a look at them.
 
It's not just the length of the pipe which is important. You have to take into account the flow rate, which depends on the size of radiator and the temperature differential. For example:

Resistance of 18m of 10mm pipe connected to a 2kW rad with a 20C differential is approx 0.58m, with a 10C differential it is approx 1.94m. The flow rate has doubled so the resistance increases by four times.

Upload your rough calculations and I can take a look at them.
It's not just the length of the pipe which is important. You have to take into account the flow rate, which depends on the size of radiator and the temperature differential. For example:

Resistance of 18m of 10mm pipe connected to a 2kW rad with a 20C differential is approx 0.58m, with a 10C differential it is approx 1.94m. The flow rate has doubled so the resistance increases by four times.

Upload your rough calculations and I can take a look at them.

I won't embarrass myself as they are obviously wrong and too basic. It's plastic pipe too which might make a difference?
 
I won't embarrass myself as they are obviously wrong and too basic. It's plastic pipe too which might make a difference?
Not wrong just has advantages / disadvantages = smoother bore less fitting but at the end of the days it is a small pipe which limits the heat flow to each rad to something like 3 - 3.5kW but each is fed directly from a 22mm manifold.
 