Want so start using them on bigger jobs we do to make balancing easier.
To set them all you do is work out the flow rate and pressure loss, match them up on the products technical chart and set it to that, is that right?
Job we'r currently doing i have worked out the upstairs heating zone which is radiators (downstairs is ufh through out) works out at: Flow rate of 0.23 L/s and have a pressure loss of 300 pa/m.
From using the technical graph for the Honeywell V5010Y0025 i set the valve to setting 3 and that would give me the correct flow rate through the circuit, right or not? I want to use the inch version as the pipes will be 28mm.
here is the link for the chart and the valve i want to use: the chart for V5010 Kombi-3-plus BLUE, DN25.
[DLMURL]https://products.ecc.emea.honeywell.com/europe/pdf/v5000-5010-pd-en0h0278ge25r0605.pdf[/DLMURL]
any others that you'd reccomend that are better?
I like the look of this one as seems simple and the price is good in BSS.
When setting them when on single emitters, for example a fan heater in a shop, is the balancing valve simply set to the maximum flow rate required by the unit?
Cheers guys.
To set them all you do is work out the flow rate and pressure loss, match them up on the products technical chart and set it to that, is that right?
Job we'r currently doing i have worked out the upstairs heating zone which is radiators (downstairs is ufh through out) works out at: Flow rate of 0.23 L/s and have a pressure loss of 300 pa/m.
From using the technical graph for the Honeywell V5010Y0025 i set the valve to setting 3 and that would give me the correct flow rate through the circuit, right or not? I want to use the inch version as the pipes will be 28mm.
here is the link for the chart and the valve i want to use: the chart for V5010 Kombi-3-plus BLUE, DN25.
[DLMURL]https://products.ecc.emea.honeywell.com/europe/pdf/v5000-5010-pd-en0h0278ge25r0605.pdf[/DLMURL]
any others that you'd reccomend that are better?
I like the look of this one as seems simple and the price is good in BSS.
When setting them when on single emitters, for example a fan heater in a shop, is the balancing valve simply set to the maximum flow rate required by the unit?
Cheers guys.