armyash

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
2,653
Went to this job today and was there quite a while, it's a baxi boiler, unvented cylinder upstairs.

I get get there, boiler works fine on ch, put how to constant nothing, light comes on at programmer but no 'click' sound. So quick job swap programmer over - no change.

but if I turn he to constant, divertor powers over. Got 240 between earth and orange and also at grey. So electrically everything seems ok. Just the boiler won't fire.

Another thing, with old programmer divertor does not power over. So this at least to me proves dodgy programmer plus another fault.

With ch running and hw valve held open cust will have hw.

technical were stumped, they said there is no reason the boiler shouldn't fire following these tests. He said try changing the hydraulic pressure sensor. Have ordered this but not entirely confident this will solve the issue.

could there still be a prob with the divertor? Actually leaning toward pcb myself but tech said it can't be that.

Also pressure on boiler is fine, and no error codes.
 
Last edited:
Im maybe getting mixed up but is it a baxi system boiler with 3 way zone valve ash ?
 
Check the cylinder stat os ok as if knackered then it wont bring the boiler on but if you manually open and put on ch then it will heat the hw,
 
It's a system boiler with unvented cylinder.
No cyl stat - unless it's built in somewhere I can't see but cyl stat is a possibility, if there is one.

There is a separate electrical thing on the cylinder something about the element and something to do with the boiler but tech said can't be those.

2 2 port div valves
 
Boiler has a pressure gauge and filling loop too.

I'm getting more confused the more I think about it
 
The element is the thermostat army, it will be wired to the 2 port valve to tell it to close when water temp is reached,
 
This the type of cylinder

image.jpg
 
some unvented tanks the stat is next immersion and others come with a litlle element /phiall thats inserted into a sock and bolted to side of tank but vthere will be a cyl stat
 
The element is the thermostat army, it will be wired to the 2 port valve to tell it to close when water temp is reached,

Ok that makes sense, not sure how to test, there was a reset but couldn't do anything with it. Wasn't getting voltage there though.
 
some unvented tanks the stat is next immersion and others come with a litlle element /phiall thats inserted into a sock and bolted to side of tank but vthere will be a cyl stat


Looks I'll be going back, I was there ages bet it's a 2 min job lol
 
Status
Not open for further replies.

Reply to Basic megaflo compact. Strange issues, no hw. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, my HW is taking longer than expected to heat up and it's getting worse. I can go 10-40 degs after 1.5 hours of only heating HW, whereas I...
Replies
2
Views
403
Good Afternoon all, I am hopeful someone may be able to offer some guidance on the following. In the home we have a gas boiler (serviced...
Replies
5
Views
529
Hi everyone I have an issue with my potterton prima boiler and would love some help. It works fine when either CH or HW are on but when they are...
Replies
27
Views
2K
Hi, Over the past few months, my wife and I have noticed a constant pulsing sound throughout the house which is particularly noisy at night (this...
Replies
4
Views
677
Good morning, wondered if anyone can advise please on a resolution? My set up at home is that I have a 4-bed detached with 21 radiators...
Replies
61
Views
5K

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock