Hi all,
Just a quick one to tax your tired brain cells.
Got a customer with one of these old beasts & i was called out to it late evening because of flashing 30 & 50 degree lights & no heating/hot water.
Had a quick look at it and nothing obvious bar an occasional drip from the diverter valve large diaphragm housing to rear housing.
Reset boiler and functioned checking microswitches - ok and boiler op was ok in all settings.
Left job and let customer know it was up & running again.
Received v.late text saying same fault so said i would pop over next evening as working all day in different area.
Could not reset this time checked continuity of several cables as well as overheat stat which had continuity.
Checked voltage to fan & non present.
Boiler is old and i was tired so - Poss pcb? or have i missed something, was too late to ring tech helpline.
Any advice is gratefully received,
Cheers,
Andy

Mentioned it might be worth investing in new boiler & that Baxi 830 was a comparable output DHW but a fair bit more efficient & cust was receptive but always like to know & understand any fault for future reference
 
aps working correctly / going to next stage??
 
Fan doesn't spin up.
Did on original reset but after that when fault re-occurred with the 30 & 50 lights usual clicks on boiler, pump runs & then diddly.
M/Switches on diverter op ok, checked the looming for continuity, used flow diagram/chart & followed.
Checked from overheat stat connector through pcb & had no continuity as per instruction. Had continuity on overheat stat itself.
No voltage at fan connections.

Don't want to throw to much more into it from previous repairs over last couple of years
 
i would say pcb then but tbh new boiler time
 
Cheers Shaun,
Was thinking it was going to end up heading down that route.
Will save the customer in the long run so will see him tomorrow about replacing the boiler.
Looking to drop a Baxi 830 in as very similar specs to the old unit, any thoughts from you guys on that.

Also got another old dear with an Ideal Mini C24 combi - pre condensing which will prob be going down the same route i think as its playing up as well.
A few more long days and some juggling customers around me thinks.
 
Not installed an 830 yet. Done a few 630s and they seem like a good boiler, can't comment on reliability as they only been installed less than a year. Isn't the 830 just a 630 with a longer warranty and a filter? To me an extra £200 isn't worth the cost of a filter and a warranty that likely won't get honoured after 7years.
 

Reply to Baxi 105e issue in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a very strange issue with my BAXI 105e DHW. if i turn on the hot tap the pump starts and demand for DHW is shown, after a some seconds it...
Replies
1
Views
518
Hi, Over the past few months, my wife and I have noticed a constant pulsing sound throughout the house which is particularly noisy at night (this...
Replies
4
Views
681
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
291
MartinPod81
M
B
Issue with boiler short cycling in system with hot water tank. We have an ideal heating logic heat2 h15 boiler which feeds a hot water tank...
Replies
10
Views
1K
Hi, I need some urgent advice. I've Just come home after going out for evening, to discover hallway floor and kitchen floor covered in water. On...
Replies
1
Views
535
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock