we recently had hot water being discharged from the tundish pipe on our boiler on a regular basis, immediately after the bolier had been on.

We called a plumber out who within 2 mins told us it must be the t&prv valves and he would need to replace them (he did not inspect anything). He came back a few days later and replaced them at a total cost of £400.

The problem persisted so we called him back. He then said he'd check the temperature setting - he checked and found them set to max and turned them down to 55oC.

This fixed the problem. However, I was annoyed as my feeling was that he should have checked the temp first as it transpires this was the problem and not the valves. Therefore, the first repair was unecessary and we wasted £400.

I complained to the Company and they have told me that having spoken to the plumber in question, the valves were faulty and needed replacing, evidenced by them letting by even when the cylinder was cold.

I dispute this as the plumber was not here when the valves were letting by - he was never here when the system leaked. Also, the system only leaked hot water, not cold.

Could someone help me to understand if the plumber has acted approrpiately and/or whether the replacement of the valves was necessary or whether the plumber should have checked the system temp settings first?

Regards
 
Things may well of been able to be done differently however you have no idea or proof of what was checked or done, you are making assumption, rightly or wrongly about what happened and maybe putting 2 and 2 together and coming up with 4 or maybe 5,unless you have the old parts, you have no proof of any of your assumptions and it would be/is your inexperienced and unqualified opinion against an hopefully experienced qualified operative
I can tell a great deal having looked at a boiler for 2 to 5 mins and there is a good argument that once this safety device has been operated it should be replaced, I would however be concerned that the thermostat was just turned down and not replaced as sounds like it is out of calibration and should be replaced

imho
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Boiler discharging hot water from tundish pipe" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
Moysey,
Last reply from
Puddle,
Replies
1
Views
3,998
Back
Top