Discuss Boiler keeps on boiling water even heating is switched off in the Central Heating Forum area at PlumbersForums.net

Messages
24
The problem is, my ideal boiler logic heat h15 keeps on burning (igniting flame icon on) all the time, all day long, regardless of the programmed on off schedule for both heating and hot water.

when we have the heating turned off from the thermostat programmer (danfoss tp9000ma-si), i.e frosted protection at 5 degree, or it is "off" during the daily program. It still burning, heating water.

When we have both heating and water hot scheduled to be off, it still burning.

I can safely say that there is no demand called from the program and it just supplies. The temperature displayed on the boiler is always 70+, I expect it displays 00 sometimes to show no demand required.

I have had an engineer check when doing annual service, boiler itself is ok, but he doesn't know what this problem is, suggested is the motorized valve, but he can't prove it is not functioning, as he seems to prove that all 3 of them are working ( 2 heat zone, 1 hot water).

So any suggestions to my problem please? How may I track down the root cause and take action accordingly?

Right now the house is always burning hot, I have to manually adjust the radiator thermostat, as well as switch off the boiler itself to avoid unnecessary heat(money)
 
Ultimately your boiler "switched live" supply is turned on and off by microswitches in the motorised valves you have, irrespective of the setting of other controls. If one of the motorised valves is stuck, or a microswitch inside is welded closed, it would account for the symptoms you describe.
Any competent plumber or electrician ought to be able to get to the bottom of the problem, through electrical testing/ diagnosis.
 
Ultimately your boiler "switched live" supply is turned on and off by microswitches in the motorised valves you have, irrespective of the setting of other controls. If one of the motorised valves is stuck, or a microswitch inside is welded closed, it would account for the symptoms you describe.
Any competent plumber or electrician ought to be able to get to the bottom of the problem, through electrical testing/ diagnosis.
So it has to be the motorized valves, can not be sensor or thermostat or programmer?

How may I isolate and identify the faulty motorised valve please?

Also, when I turned off the boiler itself, the heating system did gradually cool down, is it because the motorized valves 'working' and stop the hot water out? Or the valve still malfunction and draining all the the hot water out, since no fire is supplied to provide more hot water, so eventually all hot water drains out and system cools down?

My motorised valve is Honeywell 272848
 
Last edited:
You will have to remove the orange wire from each motorized valve at its nearest wiring centre when neither CW or HW programmed on and test for 230V between the orange wire and neutral (or earth), take care as one might be live with boiler switched off as the motorized valve (end switches) are supplied with a permanent live (grey wires).
 

Attachments

  • S Plan Wiring.gif
    S Plan Wiring.gif
    20.1 KB · Views: 12
So it has to be the motorized valves, can not be sensor or thermostat or programmer?
sorry to mislead you - the above items do need to be working, supplying power to the motorised valves for the boiler switched live to get power. So the room stat should be able to turn the boiler on and off, which you say it does.
Also you should have a thermostat on the hot water cylinder that supplies power, which should switch off when the water is hot enough. You don't mention that?
If that were faulty it might cause your symptoms
How may I isolate and identify the faulty motorised valve please?
I see John.g has answered this!
Also, when I turned off the boiler itself, the heating system did gradually cool down, is it because the motorized valves 'working' and stop the hot water out? Or the valve still malfunction and draining all the the hot water out, since no fire is supplied to provide more hot water, so eventually all hot water drains out and system cools down?
Valves don't drain the water out, they just stop/alter the flow. The water stays in the system and gradually cools down.
 
Am I right in thinking that the orange on the valves gets its supply from the permanent live(grey) to the valve not the switch live which just actuates the valve (brown).

I think a stuck microswitch will fire the boiler without the programmer/ stat calling for demand.

I personally would give a different plumber a ring and get them to find out which valve it is and get them to change it. Mention on the phone it needs a bit of diagnosis as not all plumbers are electrically clued up and find one that is. I would bet good money on a stuck microswitch.

A faulty programmer could be a culprit if you’ve left your room thermostat at an unachievable level or the valves at the radiator in the same room as the thermostat has been meddled with. A good check will be if the room thermostat reads the same temperature as you think the room should be
 
Last edited:
sorry to mislead you - the above items do need to be working, supplying power to the motorised valves for the boiler switched live to get power. So the room stat should be able to turn the boiler on and off, which you say it does.
Also you should have a thermostat on the hot water cylinder that supplies power, which should switch off when the water is hot enough. You don't mention that?
If that were faulty it might cause your symptoms

Yes, there is one, which is Codice 542794, I never touched it since day one so I just forgot to mention, it is set to 50 degree.
I am unable to find any manual of this thermostat, how to diagnose whether it is faulty pleaes?

Valves don't drain the water out, they just stop/alter the flow. The water stays in the system and gradually cools down.
My bad, i simply want to say that the valve didn't stop the water flow out and circulate in the heating system, and heat dissipated eventually.
 
You will have to remove the orange wire from each motorized valve at its nearest wiring centre when neither CW or HW programmed on and test for 230V between the orange wire and neutral (or earth), take care as one might be live with boiler switched off as the motorized valve (end switches) are supplied with a permanent live (grey wires).

At the moment, I have turned off boiler, the programmer (hence hot water schedule as well as heat schedule), and I notice that 2 out of 3 of the honeywell motorised valves, the levers have 'resistance' and when i push it to manual (ON), it returns. 1 has no resistance and loose.

Does it automatically mean this one is faulty?

I cant remember what that service engineer did but he didn't manage to prove that any of the Motorized Valve is faulty.
 
Last edited:
The valves typically have no resistance when open. Did you check with the power off?

If you did then I would suggest thats the culprit
So I turned off from the circuit box, and two remain motorised when I move the lever, one remains loose

Here are photos of the system btw, the greens show MV are at auto position, with resistance, push to manual/ON and feel and hear motor springs it back to auto.

Red shows the suspicious one where lever is loose.
 

Attachments

  • IMG_20230416_123241.jpg
    IMG_20230416_123241.jpg
    491 KB · Views: 22
  • IMG_20230416_123209.jpg
    IMG_20230416_123209.jpg
    416.1 KB · Views: 22
Last edited:
Tracing the wiring back to the valve, it might be easy enough to do by eye, if not remove all oranges, and test, with the power off, for continuity (buzzer) between the orange at wiring center and the orange at failed valve, then reconnect the 2 working orange wires.
 
Last edited by a moderator:
The valve cable is relatively short, I would trace back from the suspect faulty valve to the wiring centre then just remove this orange wire and test for 230V, orange to N or orange to earth with power on but programmer off.
 
I have removed the housing, but I am not too sure how to remove the orange wire from the MV end.

I tested continuity between orange and yellow/green(earth) from the wiring centre without remove any one of the wire, no beep.

I can see the spring operation when I move the lever of the good MV (circled green), and the suspected one, no spring action.

I really feel like swapping the motor between these two and see whether fault is carried.
 

Attachments

  • IMG_20230416_135813.jpg
    IMG_20230416_135813.jpg
    470.5 KB · Views: 18
I have removed the housing, but I am not too sure how to remove the orange wire from the MV end.

I tested continuity between orange and yellow/green(earth) from the wiring centre without remove any one of the wire, no beep.
Who said to do any of the above? I said remove oranges at wiring center (wc) and test between orange at wiring center and orange at MV - no need to disconnect the orange wire at MV.

John said test between orange and earth at wc.
 
You're not testing for continuity between orange and earth at the wiring center, you're looking for 230v.

Set the multi meter to the V~ symbol with the next highest number above 200. (if applicable for your multimeter)

You don't want to remove the orange from the valve just the wiring center.

I'm not sure that moving the head to a different body is worth doing as it won't solve your problem. You can take the head off the one that's "broken" and using a spanner try and rotate the shaft on the valve, if it rotates freely its just the motor that's knackered if its stiff then the whole valve needs changing
 
Now I have removed the suspected orange wire, and turn back power on from fuse box, but there is no light on the wilo pump, and I turn on my ideal boiler and it just stays at zero...

What have I done wrong? So far I have only removed the orange from box and open the housing of the two valves...
 

Attachments

  • 16816526299132332913211781509061.jpg
    16816526299132332913211781509061.jpg
    260.3 KB · Views: 14
So how may I probe at the orange wire at MV? I dont see any point that I can touch.
Apologies, there doesn’t appear to be a point you can touch, was thinking of a Drayton valve. Looks like you’ll have to do a live voltage test or remove the grey wire for the corresponding valve at wc and test between these, if you have continuity then it’s closed circuit and faulty.
 
You don't probe it at the m.valve, follow the black cable back to the junction box or wiring center, on of the wires fom the cable will be orange, remove it
 
There is a blue wire in that box which is a neutral, probe with red meter lead on the orange wire and the black meter cable on the terminal screw where the blue wire is, meter set to 500/600v AC.
 
There is a blue wire in that box which is a neutral, probe with red meter lead on the orange wire and the black meter cable on the terminal screw where the blue wire is, meter set to 500/600v AC.
I tried the above, got nothing, I don't seem to have any power even though I switched back from the fuse box...

You can see from the photo there is no green light on the wilo pump...

Is there any other switch in the system?
 

Attachments

  • 16816536370205417591088217794894.jpg
    16816536370205417591088217794894.jpg
    353.1 KB · Views: 11
There should be nothing on apart from power as we are trying to determine.ine if the end switch is still made on the suspect m valve
 
Yes, that is the problem, IE your M.valve is still sending a signal to the boiler/pump to run even though he M valve isn't getting a demand to open from the relevant system so needs renewing, more than likely just the actuator which doesn't involve draining down the system.

Why didnt you probe between the removed orange wire and earth with power on but both CH & HW off, it should have read 230V.
 
Last edited:
I agree with you conclusion, but base on the fact that this lever is loose.

Still trying to understand how my system is not powered up without having it to reconnect back.

I am thinking to replace the synchron motor, which I have learnt how to from youtube, seems like an easy job, and yes, no draining system need, although it is a challenge for me as you may see from my earlier photos, the faulty one is the one below and i can't even remove the housing completely.

Did a quick search on google for price and availability, what would be the difference between the 20 quids one from screwfix and 10 quids one from amazon? which one is a safe/wise choice?

1681655991225.png
 
Have never replaced the motor only.

"Still trying to understand how my system is not powered up without having it to reconnect back."
If you mean boiler/pump not running then its because there is no demand because you had removed the orange wire from the faulty M.valve, if you leave it disconnected and create a CH or HW demand then the boiler/pump will start up, is it a CH or HW M.valve thats faulty?.
 
Yes, that is the problem, IE your M.valve is still sending a signal to the boiler/pump to run even though he M valve isn't getting a demand to open from the relevant system so needs renewing, more than likely just the actuator which doesn't involve draining down the system.

Why didnt you probe between the removed orange wire and earth with power on but both CH & HW off, it should have read 230V.
Sorry, I did that, so i did measure 240V between the removed orange and the earth/neutral, while the connected orange in the box are reading 0V.

I was too focusing on why I cant turn on the system even though i had turn power on...
 
Have never replaced the motor only.

"Still trying to understand how my system is not powered up without having it to reconnect back."
If you mean boiler/pump not running then its because there is no demand because you had removed the orange wire from the faulty M.valve, if you leave it disconnected and create a CH or HW demand then the boiler/pump will start up, is it a CH or HW M.valve thats faulty?.
I get it now!!!!!

Thank you for being so patient to me!!!!!

Yes, I thought there were no power in the system, as I thought the green indicator on the pump means it is working/standby. I just disconnected the suspected orange wire again, turn on the system, boost hot water from the programmer to create demand, and boiler wakes up to work!
 
The whole actuator, at least, , as its the spring return thats probably causing the problem or the end switch sticking on, remove the actuator from the valve and switch the zone valve on off with the actuator removed and see if 230v still present when switched off, also open/close the zone valve with a adjustable spanner or such on the valve spindle, it should move relatively very easily.
 
The whole actuator, at least, , as its the spring return thats probably causing the problem or the end switch sticking on, remove the actuator from the valve and switch the zone valve on off with the actuator removed and see if 230v still present when switched off, also open/close the zone valve with a adjustable spanner or such on the valve spindle, it should move relatively very easily.

Would like to try, but did a search on youtube, couldn't find any tutorial of how to, basically i have no idea what the structure is.

You know any good youtube video i can follow please?
 
Have you tested if theres 240 on the brown for the 2 port valve in the wiring centre ?

With nothing calling eg heat and hot water timers off

You won’t get the head off as there’s not enough space to lift it out need to rotate the valve so the head sticks out front time for a plumber I would say
 
Now something I don't understand, I thought the system is actually running, but even though I boosted hot water, create demand, the boiler is not on, is always 00, I have only removed the faulty orange wire from WC, and touched absolutely nothing regarding HW, and I did see the boiler ignited yesterday for once (didn't check after), the time that I thought the system had no power.

So what is my problem now ...

When I press restart from the boiler, it doesn't seem to go through the usual start up sequence, but stays 00 all time...
 

Attachments

  • 16817195171525387490801073118752.jpg
    16817195171525387490801073118752.jpg
    216.7 KB · Views: 10
  • 16817197497376205304117597426368.jpg
    16817197497376205304117597426368.jpg
    174.4 KB · Views: 10
Last edited:

Reply to Boiler keeps on boiling water even heating is switched off in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
458
B
Issue with boiler short cycling in system with hot water tank. We have an ideal heating logic heat2 h15 boiler which feeds a hot water tank...
Replies
10
Views
1K
Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
287
Hi all I have a Vaillant eco boiler at a new house I moved into last week. It’s a combo boiler and the last boiler I had was old (and much...
Replies
3
Views
439
Heating and hot water is not working. Plenty of heating oil. I have replaced batteries in thermostat and it seems to be working ok, showing flame...
Replies
5
Views
379
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock