Hi everyone.
I have recently installed a new gloworm energy 35 kwh combi boiler. The heating and hot water is functioning fine. In the first 4-5 days , the pressure was dropping from 1 bar to 0.5 bar requiring me to top up the pressure. Its now been over a week and Ive noticed the pressure drop is less. It may drop from 1 bar to 0.9 bar in 2-3 days.

Is this normal? I contacted the vaillant helpline who told me top up of pressure should only be required 2 times a year.

Is this normal or abnormal?

Thanks
 
If the pre charge pressure is also 1.0 bar or more then the filling pressure of 1 bar will result in a relatively big pressure drop with virtually no water loss. Would suggest increasing the filling pressure to 1.3 bar with a cold system and monitor it (cold) for the next few days or so,
[automerge]1601290046[/automerge]
I think that the pre charge pressure for your boiler is 0.75 bar and if it has been checked before installation then you are losing ~ 0.5 litres each time the pressure falls from 1.0 bar to 0.9 bar so if this continues you definitely have a leak somewhere, also when system heats up just ensure that the pressure isn't > 2.5/2.8 bar.
 
Last edited:
Check for obvious leaks (exposed pipework/magnetic filter/rad valves). Monitor it for a little while longer. Could just be air coming out of the system through the boiler air vent.
 

Reply to Boiler pressure normal or not in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

the pressure of my boiler looks unstable After i re-pressurize to 1.5 bar, using tap is ok without problem. but when turn on the central heating...
Replies
0
Views
426
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
520
losing pressure
L
Can central heating / gas engineer expert help me with below issue. During winter time only, I have been having issue with low pressure or...
Replies
0
Views
617
My Grant combi oil boiler is giving me quite a headache at the moment. When I returned home last Friday I'd no heating or hot water. An engineer...
Replies
3
Views
593
Hi, I'm looking for a water pump to pump water from a storage tank at a constant 3 bar pressure. It's at a campsite I run that's at the bottom of...
Replies
2
Views
167
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock