Discuss Can a conventional system boiler be a closed system? in the Central Heating Forum area at PlumbersForums.net

Messages
18
As per the title?

I've only ever seen domestic system/conventional system boilers with an F&E tank and combi boilers which are closed systems.

Is there any reason a system boiler cant have an expansion vessel fitted and be made a closed system?

Or

Is there any reason you couldn't install a combi with an open vent/F&E?
 
The following applies to the UK and its regulations:
1. You can have sealed systems with combi (always sealed), system boilers or open vent boilers provided the manufacturer allows this - these days they nearly all do.
2. You can't really run a combi boiler off an F&E tank, as the pressure is unlikely to be sufficient to pressurise the system. Also, you'd lose the benefit of mains pressure hot and cold.
 
You would need to consult the manufacturers installation manual for that particular boiler.
I have seen all manner of configurations over the years but the manufacturer is the place to start if you're thinking of altering or installing something.
 
The following applies to the UK and its regulations:
1. You can have sealed systems with combi (always sealed), system boilers or open vent boilers provided the manufacturer allows this - these days they nearly all do.
2. You can't really run a combi boiler off an F&E tank, as the pressure is unlikely to be sufficient to pressurise the system. Also, you'd lose the benefit of mains pressure hot and cold.

Hadn't thought of the system pressure, that makes sense with a combi.
[automerge]1597826034[/automerge]
You would need to consult the manufacturers installation manual for that particular boiler.
I have seen all manner of configurations over the years but the manufacturer is the place to start if you're thinking of altering or installing something.

It was more out of curiosity as a newbie, @stedysons comment on pressure makes sense with the combi.
 
As per the others a consultation with the manufacturer would be a worth while chat. This is an extract from the Intergas (Netherlands based) eco rf30 manual which gives different configurations:
 

Attachments

  • D53A57C6-08D9-4FF0-946B-079B845C1A20.jpeg
    D53A57C6-08D9-4FF0-946B-079B845C1A20.jpeg
    26.4 KB · Views: 13
The following applies to the UK and its regulations:
1. You can have sealed systems with combi (always sealed), system boilers or open vent boilers provided the manufacturer allows this - these days they nearly all do.
2. You can't really run a combi boiler off an F&E tank, as the pressure is unlikely to be sufficient to pressurise the system. Also, you'd lose the benefit of mains pressure hot and cold.

Why does a combi boiler require pressure to operate yet a system boiler doesn't?

Is this a protection mechanism or is it designed to increase the boiling point of the heating medium?
 
Why does a combi boiler require pressure to operate yet a system boiler doesn't?

System boilers do require pressure to operate, it’s heat only/open vent boilers that do not. A sealed system only gets rid of the feed and expansion cistern in the loft. It can be fed onto a gravity hot water system or an unvented cylinder.
 

Reply to Can a conventional system boiler be a closed system? in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig...
Replies
3
Views
553
I think the last discussion was back in 2021. A few questions to guide any discussion. Which are the cheapest to heat over the year, system or...
Replies
3
Views
414
Hi all, Got a nightmare situation with a central heating system I recently adopted. It's an open vent system with a combined F&E pipe, with a...
Replies
17
Views
2K
Hello, I live in a two floor semi with a gravity fed conventional gas fired boiler (Potterton Kingfisher MF). The boiler is fed cold water from...
Replies
0
Views
521
Hi all, We're looking to update our existing central heating setup and wanted to get a few more opinions. We currently have an open vented...
Replies
11
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock