tommyg01

Hi All,

I am looking to do away with a horrible looking Gully/Drain outside my side door (actually used as the front door). The kitchen sink waste pipe comes out through the wall just above the gully/drain and I am hoping, I can just extend the pipework around the wall and do a cut in on the soil pipe. Is this allowed regulation wise? Would I need to run the pipe at a slight slope downwards going towards the stack?

TIA

Tom
 
If course you can. If the soil stack is already built then you use one of these to connect it in.

110mm Strap on Boss Adaptor (50mm Ø Boss)

You can buy reducers that sit inside the boss to reduce the 50mm Diameter boss down to 40mm for a kitchen sink waste pipe.

The required falls are all written down in Part H of the Building Regulations but go with a fall of 18mm per metre and you will be fine. Remember to clip it to the wall to stop it sagging over time.
 
Last edited:
That's good news, all I have to do now is find a website the sells all the bits (pipe, brackets etc), in Grey and delivers.

Thanks

Tom
 
If you end up modifying underground drainage this work is notifiable to Building Control as it will need to be tested properly prior to backfilling. Clearly to remove the gully you will have to modify the drains! Forgot to mention this before!
 
If you end up modifying underground drainage this work is notifiable to Building Control as it will need to be tested properly prior to backfilling. Clearly to remove the gully you will have to modify the drains! Forgot to mention this before!

Oh that's a pain. I have 2 gully/drains in a small courtyard area, 1 of which I planned to seal over. I guess I will have to ask my local building control.

Thanks

Tom
 
If you end up modifying underground drainage this work is notifiable to Building Control as it will need to be tested properly prior to backfilling. Clearly to remove the gully you will have to modify the drains! Forgot to mention this before!

Your wrong there. No test required when connecting to existing unless it is chambered at the connection which isn't necessary either.

As far as building regs in England go with this one i'm not sure but up here it wouldn't be notifiable.
Then again we don't need to notify boilers either.
 
Your wrong there. No test required when connecting to existing unless it is chambered at the connection which isn't necessary either.

As far as building regs in England go with this one i'm not sure but up here it wouldn't be notifiable.
Then again we don't need to notify boilers either.

Emailed my local council this evening, let's see what they say.

Tom
 
Status
Not open for further replies.

Reply to Can I run the kitchen sink waste pipe, straight into the toilet stack outside? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and...
Replies
2
Views
183
Sonya K
S
Just started gound work on self build bungalow and wondering best way to do below ground soil pipes. For toilet I was going to go straight down...
Replies
2
Views
190
Hello I am looking to install a slimline dishwasher (integrated) into a cupboard in my kitchen. The depth of the dishwasher is 550mm and the...
Replies
22
Views
689
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
369
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to...
Replies
6
Views
325
Back
Top