Discuss CH Boiler Drain cock in the USA area at PlumbersForums.net

Messages
8
Below my Boiler I have a Pressure Relief Valve which vents to the outside and a drain cock (see image)
The drain-cock is dripping and requires a new washer
If I release this drain cock
Will it just drain down until the Expansion Tank pressure drops to 0bar until no more water flows
Or
Will it drain down the entire CH system ( my worst nightmare)
 

Attachments

  • IMG_20201018_101036922.jpg
    IMG_20201018_101036922.jpg
    1.1 MB · Views: 20
It will drain the entire heating primary system
 
Drain the pressure to zero. Put bucket under drain cock. Close boiler isolation valves.

Whip out the spindle and washer. Quickly refit.

For a bit more time, get a second pair of hands to put the fingers over the drain cock outlets while to attach the new washer.
 
I have been succesfull. I have no isolation valves on the boiler
I closed both valves eitherside of the pump and released the drain cock
Water drained until ZeroBar and then stopped - Pipe dry
Changed tap with no problem,

Thanks for your advice
 

Reply to CH Boiler Drain cock in the USA area at PlumbersForums.net

Similar plumbing topics

Hi I have a baxi duotec combi boiler that every day or other day needs topping up as pressure drops below 0.5bar. When fired up it can reach...
Replies
2
Views
473
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
410
Hi folks my partner has a Greenstar 30Si boiler, the pressure is just below 3 bar but for the past year or so water has been slowly dripping out...
Replies
6
Views
716
I just bought a Biasi 25c Combi boiler and I can't understand what the Main Circuit Drain Valve is for. It has a screw in plastic end so doesn't...
Replies
4
Views
1K
Advice please. I drained my open system to add x800 a couple of weeks ago and all ran smoothly. Last night I drained it all out, cleaned the tank...
Replies
28
Views
4K
Back
Top