Thanks for that. it is saying i need 21 Kwatts.
That's a lot of heat for a three bed house. Is it very large or very old with no insulation, eg solid walls, single glazed sash windows etc.
As you have a semi, the number of front to back walls is only 1. Did you enter 2 by mistake
What will happen if i run it on 15 ? It was set to 20 my the engineer and that was fine. i was thinking of turning it down to 15 you see.
The worst that can happen is that the house will not get warm enough.
I am not sure what modulating actually means.
Older boilers had a fixed output, which could often be adjusted by the installer to meet the specific requirement. These were know as range rated boilers. Control over the water temperature was by a thermostat, which is just a switch which turns the boiler on and off to maintain the required water temperature. When the boiler was on, it ran at the set output; when it was off, the output was zero.
With a modulating boiler the output is continuously variable between the min and max. Instead of having a thermostat, a temperature sensor is used. When the boiler reaches the required temperature the output of the boiler is automatically reduced so the required water temperature is maintained. The boiler only turns off if the boiler cannot modulate low enough.
Range rated boilers are like a dodgem car - it either goes or it stops. A modulating boiler is like a car with an accelerator - you use it to adjust the engine output to maintain the required speed.
yes my boiler is fully modulating. so why do they have a range rating facility on them in the first place?
To prevent the maximum output exceeding the maximum requirement of the house. When a modulating boiler ignites, the output is set to maximum and then reduces. If the maximum is much higher than required, the temperature of the water can rise so quickly that the boiler shuts down, waits for the temperature to drop and then tries again. The result can be that the house takes ages to reach temperature, if it even gets there. This is particularly true of combi boilers where the requirement for hot water could be as much as 40kW, while the house may only need 10kW. The max heating output of a 40kW combi boiler may be 30kW.
Another problem, particularly with large combi boilers, is that the minimum CH output may be above the CH requirement of the house. In this case the boiler cannot modulate low enough, so the boiler reverts to on off mode.
Lastly, the required output of a boiler varies with the weather: colder= more output, warmer = less output. The boiler is always sized for the worst conditions, normally an outside temperature of -1C. This means that the boiler needs to modulate lower if the outside temperature is higher than -1C.
If the lowest output of the boiler is only slightly below that required for a -1C temperature, then, in warmer weather, the boiler will revert to on-off mode.