Cold water tank in the attic overflowing

Discuss Cold water tank in the attic overflowing in the Plumbing Jobs | The Job-board area at PlumbersForums.net

GGg

Messages
45
Hi All,

Looking for some advice. The tank in the attic has been trickling out of the overflow for a few weeks now.

I have an open vented system with a hot water pump (Stuart Turner monsoon twin 3) fitted.

Have already changed the valve and float in the attic. Set it very low but water is above the float. Tested it fine know it shuts off the feed that way.

Also changed the thermostat on hot water cylinder, so tank isn’t getting too hot and venting over.

I do have a shower fitted with mains cold and tank fed hot. (Plumber at the time said it would be fine because hot water is pumped) as well as 3 other mixers in the house with same hot/cold set up.

Looking online could it be the hot water is being overpowered by the cold, with mains then backfilling down the hot water pipe and filling the attic? I can see this can be resolved with a non return valve? And instead of fitting 4 non return valves can I fit one 22mm NRV on the flow from the pump? (Not the feed as this stops any ability to vent)

Thanks and sorry for the long winded post.
 
Yep agreed. I’m just going to put a NRV on the outlet from the pump for the sake of £5 and my brain exploding. Will update after fitted.
 
Ok so NRV fitted. Isn’t coming back into the tank at the moment but maybe because I turned off. Will check it over the course of the day to see if it’s come back. Thanks again for your help will keep you posted.

34802FEB-9309-42B9-B4E7-AE1428892E5D.jpeg
 
The small tank will fill your central heating the big tank fills your cylinder. Assuming it’s piped correctly the only place these to waters come close is in the coil in the cylinder, central heating water inside, domestic hot water outside. There could be a small pinhole in your coil meaning that when it heats and expands water from the smaller tank is able to pass into the domestic hot water. This then effectively makes it all one circuit no longer separate so the two tanks in the loft will try and achieve the same water level. This will only be the case though if the water level in the smaller tank is higher than that in the larger tank otherwise the same would happen only in reverse
Have traditional vented indirect system, in my case F&E tank base same level as large tank, so top level below, F&E tank overflows/steady trickle, maybe one bucket every 3 hours, also somewhat brownish water (water from taps crystal clear), guess it is coil, or could system be too hot (at one stage hot water was VERY hot), any suggestion?
 

Reply to Cold water tank in the attic overflowing in the Plumbing Jobs | The Job-board area at PlumbersForums.net