I've just had a back boiler removed and combi boiler installed and have noticed that my radiators are heating up when using the hot water. I've been told this is due to the residual heat being moved around the system once the hot water is satisfied. But the radiators are heating up as soon as i start to use the hot water not afterwards unless i turn off the TRV's on the radiators. I've checked the position of the diverter valve via the boiler and it says it's in position 2 (DHW).

Any idea as to what's going on here, I'm i right in thinking that something isn't quite right with the install or is this normal?

much thanks for any advice.
 
They do dump the heat into the rads after a hot water cycle but shouldn’t do it at the same time

What boiler do you have ?
 
Viessmann’s have had a few issues with the diverter valves best to phone them up for a warranty call
 
Viessmann’s have had a few issues with the diverter valves best to phone them up for a warranty call
I did initially suggest that to the engineer that installed it but he said it wouldn't be that. But this time i'll mention the fact that the radiators are heating up as the hot water is being used and not afterwards. Hopefully he'll take a closer look at it.

Thanks for your input.
 
Don't know if this will prove anything or not but think about it, with both CH and DHW off (boiler off) open a HW tap to give a small flow of say 1LPM but not high enough to fire the boiler, then switch on the CH and see if the water still runs cold.
 

Reply to Combi boiler install doesn't seem quite right. in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Milky hot water. Recently had a Viessmann 100-W combi boiler installed. Now when the hot water reaches any tap it is very 'milky'. This appears to...
Replies
1
Views
387
Trying to find out exactly what happens when my system boiler is called to supply the radiators and hot water cylinder at the same time. For...
Replies
7
Views
515
Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the...
Replies
5
Views
278
I've got a non condensing Glowworm Ultimate with gravity tank and hot Water tank in a 4 bed house. 11 radiators 1 double 1400mm length 1 P+...
Replies
7
Views
549
I have a heating system comprised of skirting radiators that form part of a loop from the boiler, round the house and back. Some rooms get...
Replies
1
Views
150

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock