Hi there,

Disaster has struck this morning, during the coldest week i've seen in years.

It appears as though we no longer have any hot water or heating due to a fault with the combi boiler.

We own a i-mini 24 system and the error code which we are seeing is F-2. I have looked this up in the manual and it says the following:

Flame Loss:

1. Check other gas appliances in the house are working to confirm a supply is present in the property.
2. If other appliances do not work or there are no other appliances, check the gas supply is on at the meter and/or pre payment meter has credit.

The issue here is that we don't run any appliances on gas in the house, and we also don't use a meter. I have checked with our supplier and we are actually in credit.

Does anyone know what the issue could be here? Any help would be greatly appreciated.

Thanks

James
 
Your condense pipe outside may be frozen. Get your self a gas safe Engineer to unfreeze for you. I would say try to do it yourself but you have an Ideal so probably best to get an engineer out.
 