Had a quote for complete new CH system including Worcester Greenstar 28i Junior.
Not sure I totally understand this, hence asking here: I was pretty surprised at how small the rads spec'd were as I thought condensing boilers needed as low a return temp as possible? The installer (WB accredited) is telling me that once the boiler gets going there will be hardly any difference between flow and return temp, and the rads are rated assuming flow temp of 75C.
Am I mis-understanding or does this seems far too high? Indeed the boiler's user guide suggests running the CH at between 1 & 2 on the dial - around 50C - and it also says "the radiators may need upgrading", which I assumes means "replaced with bigger ones!".
Hi Rory - Do you have concerns about the installer? If not then trust his professional decisions; if you do then get other quotes IMHO :)
My opinions:
28i Juniors aren't very good. I'd recommend going for a Worcester CDi (if you want Worcester) unless it is a flat/rental property. Personally in that price range a Vaillant Pro 28 installed by a Vaillant Advance installer (5 year warranty instead of 2) is a much better buy.
Unless you live in a very large property I wouldn't worry to much about F+R temps. You can size the radiators yourself by googling 'radiator sizing' and measuring your rooms.
Worcester Accredited means absolutely precisely nothing. Just means he installs a fair few boilers. It is no indication of quality, and in most cases you are paying for that extra warranty indirectly. Just so you know.
Condensing boilers operate at maximum efficiency with a low return temp.
Most radiator manufacturers quote a delta which is based on temps for non condensing boilers and need calculating but with some this is changing.
Typically a lower delta will in effect increases the size of the panel.
Ill see if I can find a link that explains in more detail a little about the general idea
http://blog.tradeplumbing.co.uk/the-mystery-of-delta-t-revealed/
Sort of a bit here.
But to be frank I think delta 50 is even too high.
Delta 40 is getting there more where condensing boilers need to be.
And some heating engineers even calculate more towards a delta t of 30-35 ish.
Simply put if the return temp is too high the boiler wont condense fully and the efficiencies will not be realised
Thanks for the responses.
[FONT=&quot]Do I have concerns about the installer? Hmmm….he’s very local, recommended etc. I’m confident he can do the job, I’m just not sure he “got” the more technical aspects. I did get other quotes but central heating installers seem to have very strong and fixed opinions![/FONT]
[FONT=&quot] [/FONT]
[FONT=&quot]Re the boiler – I understand the 28i Junior was updated last year. The installer says they fit a lot of them and will be guaranteed for 8yrs (although if it fails even at that point I’ll be a bit dismayed). Other installers said they wouldn’t touch WB with a barge-pole. One said he only fits Glow-worm – not a name that comes up much in discussions these days – take it or leave it.[/FONT]
[FONT=&quot]Thanks for the link about Delta-T. I used to be an industrial electrician, although I’m well out of trade now, but I’m used to having to calculate stuff like this – you can’t just throw a long bit of cable in and hope for the best! My reading is that you really need to substantially oversize rads to be able to run at lower flow temps.[/FONT]
[FONT=&quot]One of the issues with the current installation (which might be single pipe) is the return gets very hot, very rapidly, so the boiler shuts off for 3 mins and everything goes cold. Rinse and repeat. This means the house gets warm in series of very brief steps. I explained that to the installer and I really want to make sure that doesn’t happen in the new system.[/FONT]
How old is the house, how large and how well insulated?
Did the installer do a detailed heat loss calculation? Has he provided this info? If not ask for it.
1. The return needs to be below 55C for any condensing to occur.
2. The lower the return, the more condensing occurs.
3. If a flow of 75C has been assumed and a return of 55, the rads will be producing about 85% of the output given in the catalogue, so the have to be "oversized" by 17%, say 20% for safety.
The boiler should modulate and adjust pump speed according to the heat demand and keep itself condensing. Trust your installer. Your property will be loosing more heat than you will save through flue gases.
But the idea is to recover latent heat as it will save money. If my can had a hole in the fuel tank I wouldn't drive fast just because the losses from the leak exceeded what I could save by driving sensibly? What an odd argument?
In most cases the boiler will modulate to keep the flow temperature constant at whatever value the installer/user has set. Most systems with modulating boilers do not have variable speed pumps.
Thanks again all.
The house is a decent size early 1970’s 3 bed end-terrace. It’s double glazed. Gable wall is cavity insulated. Has a lobby rather than a hall so the front door basically opens straight into the living room. However, like many houses of this age and older, they weren’t designed to be sealed boxes so it’s kept well ventilated.
The installer did measure the rooms and used a rad size calculator but came up with that seem to me to be very small sized rads, especially in the bedrooms. At the moment I’ve convinced him to use larger ones more based on appearance than anything else.
The Junior doesn’t have a modulating pump but other WB models do. I did wonder about this – like all aspects of CH systems, there seem to be very polarised opinions on whether modulating pumps are a good thing or not!
Maybe its because I only fit the high end boilers. Some will learn the system size and modulate accordingly thus keeping it at optimum dew point for longer. Oversizing rads is fine but will cause intense heat up periods. Balancing the system will help a lot with better condensing. I would personally go for the best boiler and controls you can afford.
Bear in mind bedrooms have a lower design temperature of around 18 celsius. No doubt he will have sized the rads correctly but of course you can always ask for larger.
Honestly, i'd steer clear of the Worcester Juniors.
Very interesting thread.
Can someone, given the time, write a Master Class thread explaining to people like myself exactly what's what when it comes to sizing and the various problems that may occur and be thrown up with this type of install.
I agree to a degree that some boilers will modulate down to a point.
But there are limits to this.
Like ermys car fuel economy analogy...there is a sweet spot and this needs to be calculated.
2 scenarios of many...
Radiators too small so to achieve flow return heat loss you start to close trvs but then room not hot enough.
Then you shift the problem elsewhere - I.e. to the boiler cycling and not operating at a continuous low gas rate and condensing.
Radiators too small - so to keep room warm you turn rads up and the boiler doesnt condense as the flow return not enough differential and operating at non condensing.
Building fabric Heat loss, boiler size. Radiator size. Pipe size..these need to be in harmony.
Radiators too small (or stupidly too large) and you will discover the limits of your boilers modulation.
Instead of running at its lowest rate and in continual condensing mode is will literally cycle on and off and not condense as it should.
So would i be lax and presumptuous with rad sizes falling back on boilers modulation to take care of poor heating design - nope.
@wetdrip here you go:
Step 1) Do the heat loss calcs - that is a master class in itself taking into account design temperatures, u-values (insulation) (walls, windows, doors, ceilings, floors) Air change factors, degree days, constant / intermittent heating...... -
That will define both the POWER required from any heating source (aka boiler) for the heating and the approximate annual energy bill (on a room by room and total basis)
You'll be suprised how low that will be for the house in question compared to the boiler sizes most "PLUMBERS" would fit.
Why not go and do the three day logic course on Domestic Heating Design... - see details below.
Step 2) You now need to add in the power requirements for the domestic hot water requirements, taking into account reheat speed, design the DHW cylinder to match.
Step 3) Now based on your heat source and emitters (boilers and rads / underfloor) design your flow and return temperatures.
Step 4) Now you know your average flow temperature, taking into account the room temperature you've got your delta T for the emitter design
Step 5) Download the Stelrad book: http://www.stelrad.com/wp-content/uploads/2014/08/stelrad_radiator_book.pdf from there you can look up the power required for a given delta T and choose your rads.
Step 6) Design the hydraulics (pipe sizing and layout) to meet the flow volumes required to meet the heat loads in each of the rads
Step 7) Design the control systems to meet the customers needs and various temperature zones.
Step 8) Produce a quote.
and then lose the job to the cheapest bidder who just walked around with a notebook and does a *** packet calc that sounds good and who installs a system that will never work properly.
We have yet to visit ANY property that has the existing rads properly sized for their heating system.
Rads too large cause problems, rads too small cause problems, oversized and undersized boilers cause problems, badly design controls cause problems.
But then I only wanted you to replace my (old inefficient, broken) boiler...
Here's you starter for 10:
Logic : Plumbing & Heating: Design and Specify Foundation Course (5 Day inc. WRAS, G3 Unvented and Energy Efficiency
Course Outline
• U Values: understanding what they are and their use
• Whole-building design heat loss calculations
• Comfort conditions and basic heating and hot water principles
• Basic heating & hot water system types
• Ventilation & air movement: principles and basics in practice
• Domestic system design
• Understanding TACMA and Part L regulations
• Storage units: comprehensive detail on specifying
• System specification including emitters, pipework, boilers and pump sizing
• Sizing and selection of hot water systems
• WRAS Water Regulations
The course is designed to give you a good level of understanding which will allow you to design and specify basic domestic heating systems and size hot water storage cylinders.
This 8-10 day course has built into it the Logic Certification Foundation Course in Heating & Hot Water Design and WRAS Water Regulations and G3 Unvented.
Certification
Logic Certification - 3 Qualifications
Plumbing & Heating design Foundation
G3 Unvented Hot water
Water Regulations
Ok so hear goes I work my room heat losses out @ delta 50 1 degree = 2% i up size by 20% which gives me a delta 40 heat figure for each room. I then work out the system requirement and add 10% for pipework heat loss. I range rate the boiler through the perameters at a Max of this figure. I set flow temp to 65 allowing room temp to be 15...... Delta 40! Completely balance the system for equal heat loss per rad and fit an external weather compensator. Fit a fully modulating boiler with adjusting pump speed and system learning capabilities and there you have it the most condensing system you can get. This will cost you mind and most are not willing to pay for this level of service!
Or take the C&G 6089 Level 3 which includes all of the above, at a good training establishment of course.
80% of customers only want a working heating system and a powerful shower.
10% want A 937 or megaflow because their friend has one... in his 1 bed flat in Chelsea.
The final 10% want the best and are like you Rory.
Hats off to you for asking the right questions and doing your own research. Ask your installer these questions and see what he thinks. His answers will let you know if he is the type of installer you need.
If not be prepared to pay a bit more for someone who is.
Thanks for the compliments! I wouldn't say I wanted the best, but optimising the rad sizing doesn't cost much and seems quite important with a condensing boiler. As best I can gather, it would be better to err on the side of over-sizing.
I think I'm paying a very fair price for the job - certainly it's not being done cheap.
My opinions:
i would not fit a vaillant myself, we all have our own ideas what makes a good boiler and manufacturer.
what makes a vaillant advanced installer better than a worcester accredited installer out of interest?
As for rad sizing, you can do this yourself on the internet at loads of places, if you want to do it long hand get a book and have a go. If your old rads have no convectors/fins then a new rads of the same size will give more ouput if your were comparing apples to apples (with fins:)).
Your the customer at the end of the day, you can take the advise of your engineer but if you want a larger rad as your the person paying and lives in the property then that what you should have. You can make it as complicated or as simple as you want, your paying you have what you want.
Didn't say it was 'better'. WA installers give longer warranties, which in many cases they (aka you) are paying for. VA installers can give longer warranties for free.
yes but they steal your service work...
Just to throw something else into the mix Rory about your boiler selection & controls, are you aware of Weather Compensation a few of the boiler manufacturers have this already built into the electronics so with a low cost thermistor kit it can be activated.
I would recommend this as it will work nicely with your new system, it basically varies the water temp to suit the outside temp thus keeping the boiler in condensing mode for longer periods without effecting the comfort levels. (why is it in there? cos in a most of europe it has to be installed & working).
Can I say, it would be nice to have a more customers who took such an interest in there heating systems, as it might start to raise the standards of design in the domestic industry let along the installation quality.
Assuming that delta X is the difference between room temperature and the mean rad temp [(flow+return)/2], then unfortunately a 20% drop in the delta does not give a 20% drop in the rad output; it's nearer to 25%.
That assumes the return is 45.
But what if the customer doesn't want his house at 15? Answer: your rads will be undersized by 20%.
Output of a "1 kW" rad at different temps:
75/65/15 = 1.14 kW
75/65/20 = 1.00 kW
65/45/15 = 0.73 kW
65/45/20 = 0.60 kW
75/65/15 = 1.14 kW
75/65/20 = 1.00 kW
65/45/15 = 0.73 kW
65/45/20 = 0.60 kW
Modern design recommendations on design room temps Rad's = 21deg C U/F = 20deg C
I use 21 (for rads) in all rooms, easer that way.
As Chris has mentioned wether comp, IMO it's an absolute must , the sensor for my boiler at home was approx £100 (viessman 200) it's nicked plenty off my gas bill, the big thing if you go for it your house must be WELL insulated.
To use it you strangely have to rethink the way your heating system works, ie her indoors constantly telling me the rads aren't hot, my reply , are you warm , answer yes, is the house warm , answer yes, = low gas bill .
75/65/15 = 1.14 kW
75/65/20 = 1.00 kW
65/45/15 = 0.73 kW
65/45/20 = 0.60 kW
15 is the starting room temperature allowing up to 25 which would give a room to rad difference of 40