Hi all,

Excuse the length but this seems like a complicated fix.

I lived in a 1930s block of flats. Brick building with concrete slab floors.

The waste stack is internal and bricked into corner of the bathroom. I noticed paint peeling and brown staining recently at the bottom near the floor, and I opened up the riser and see whats going on.

Turns out there's two leaks - a big ish one on the bath waste water pipe coming down form the upstairs flat, that leads into the cast iron stack. This one has been fixed with fernco and a new small section.

There also is a leak on the length of lead piping that goes into the stack itself. The leak isn't visible, but it seems to be on or around the wiped joint where a lead waste pipe couples straight into the cast iron.

The cast iron runs the up and down the whole building, with all flats being the same layout, however because the flat above me is in the mansard roof and is inset, it looks like the waste pipe converts to lead in my flat before going up into the concrete slab floors as a lead soil pipe. see diagram.

It seems the obvious thing would be to get rid of a lead section entirely. The only problem is the lead goes up into the poured slab above and then serves that flat before appearing again as a vent sticking out of the roof. Renewing all of the lead section would involve massively taking apart the flat above's bathroom and the roof to the block of flats.

The waste pipe is the responsibility of the council, and their plumber from Mears came round and doesn't know how to fix it. He seems to say that you can't chop out the cracked section of lead and renew just that section, because of problems attaching the new section to the good section of lead. Fernco apparently might not make a good seal because the lead might not be perfectly round. Going into the cast iron end is fine, but connecting to the lead before it dissappears into the ceiling is the issue.

The plumber caked the problem area in CT1 and Denso tape and says that's all he can personally do, without referring it back to the council. The leak is about 50% better.

(For ease, in the diagram I have not drawn the smaller fernco-solved bath waste pipe which was copper into the iron)

Perhaps it's wishful thinking, but the larger leak lead me to find this smaller leak, which I don't think I would have even known about. It's a soil stack leak and so is gross, but it is not leaking that much. Part of me wants to just box it back in. It dribbles down the cats iron, but not so much that it reaches the floor, so the floor will no longer be getting damp. Provided this lead leak doesn't get worse.

Does anyone have any ideas?
 

Attachments

  • IMG_6513.jpg
    IMG_6513.jpg
    256.4 KB · Views: 25
  • IMG_6491.jpg
    IMG_6491.jpg
    479.6 KB · Views: 19
Need to replace the stack as it’s getting old and starting to cause problems
 
Realistically, the pipe isn't under pressure. While I see the point about the lead may not be perfectly round, I think that if the lead, or a new continuation from the lead were to go INTO the cast socket rather than rely on sealing to the outside of the socket, water would stay inside. Which may leave the possibility of sewer gasses escaping but any leak of foul air could then be sealed externally with LSX.

It's not do-able to make the joint in your flat as you are so close to the ceiling. The plumber could potentially cut the cast iron lower down, or, alternatively, replace a section of pipe from upstairs down to your socket and joint to the lead on the floor above.

You could get a skilled worker who could weld up lead? Us youngsters, sadly...

Or, realistically, it may be cheaper to look at a new stack, as Shaun has suggested. Goodness knows why people think hiding things inside walls is a good idea. Makes maintenance very hard.
 
Realistically, the pipe isn't under pressure. While I see the point about the lead may not be perfectly round, I think that if the lead, or a new continuation from the lead were to go INTO the cast socket rather than rely on sealing to the outside of the socket, water would stay inside. Which may leave the possibility of sewer gasses escaping but any leak of foul air could then be sealed externally with LSX.

It's not do-able to make the joint in your flat as you are so close to the ceiling. The plumber could potentially cut the cast iron lower down, or, alternatively, replace a section of pipe from upstairs down to your socket and joint to the lead on the floor above.

You could get a skilled worker who could weld up lead? Us youngsters, sadly...

Or, realistically, it may be cheaper to look at a new stack, as Shaun has suggested. Goodness knows why people think hiding things inside walls is a good idea. Makes maintenance very hard.

Thanks for your input. I think there’s enough by the ceiling to couple to the lead although the image doesn’t show it. I see that if the new pipe could go INTO the cast iron then that would work on that end.

The question is what would you use to couple to the lead?

I think if we replace the lead on the floor above we would have the same situation of how to couple to lead pipe this large.
 
First, ensure the exact position of the leak on the lead is found.

If in a workable area, cut lead just above/through leak.

Remove lead from cast socket.

Cement a section of plastic soil into cast socket.

Join lead and plastic with a Fernco or time saver coupling.
 

Reply to Difficult leak on waste stack in block of flats in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
186
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
127
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
1
Views
39
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
243
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock