Hi, I'm new here and appreciate any help or ideas on the below.

I suspect there's a underfloor leak as I have a damp patch on the wall, rotten floorboards and skirting boards between the bathroom and the living room. Leak tracing (gas, thermo, acoustic) concluded there is no leak despite the pressure tests indicating a drop in pressure.

The pressure test is done by connecting the gauge instead of the washing machine and normally on shutting the stopcck the pressure drops from 2-2.5 bars (while no taps or toilet are leaking) to 0 in around 1 min. However lately I realised that when doing the pressure test first thing in the morning (before using any water) the pressure does not drop. After the use of taps or flushing the toiler the pressure again starts dropping rapidly.

It is a one bedroom ground floor flat with a combi boiler.

Could these changes in pressure be caused by a water leak or should I look elsewhere?

Many thanks
 
Last edited:
Try not to jump to conclusions too soon, but the morning result suggests that there is a low probability of a leak in the cold water pipework. (Not 'zero', just 'low' because some leaks are temperature dependent.) That just leaves the hot water, central heating, drains, penetrating damp, roof leak, condensation, failed damp-proof membrane, etc. to consider.

Who did the 'leak tracing' and what exactly did they check? When they didn't find a leak, what did they advise as the next step?

What shape is the damp area on the wall? Is it an external wall or internal?

Is the central heating losing pressure?
 
Try not to jump to conclusions too soon, but the morning result suggests that there is a low probability of a leak in the cold water pipework. (Not 'zero', just 'low' because some leaks are temperature dependent.) That just leaves the hot water, central heating, drains, penetrating damp, roof leak, condensation, failed damp-proof membrane, etc. to consider.

Who did the 'leak tracing' and what exactly did they check? When they didn't find a leak, what did they advise as the next step?

What shape is the damp area on the wall? Is it an external wall or internal?

Is the central heating losing pressure?

Hello Chuck,

Thank you for your reply.

It was plygon who did themal, acoustic and gas tracing and also sampled the plaster from where the damp patch is and the result was a mixture of salts so inconclusive. They did not advise the next step but only reported to the insurance company that they couldnt find a leak. It is an internal wall and the damp patch is horizontal around 1m above the floor (picture attached).

The central heating is not losing pressure but this morning I repeated the pressure test. The pressure again was not dropping first thing in the morning, I repeated the test after running cold and hot water (after running hot the pressure actually went up but think it was as the boiler was still running). After flushing the toiler and waiting a bit, the test was run again with the pressure dropped rapidly. Repeated the test later and the pressure dropped quickly again.

I am now planning on fitting a stop valve next to the toilet and use dye to monitor. I'll update as soon as I have more details.
 

Attachments

  • PXL_20201016_155117990.jpg
    PXL_20201016_155117990.jpg
    71.9 KB · Views: 11
Hmm. Is there another flat above you? Where is their bathroom located? Is there a shower right above the problem area by any chance?
 

Reply to Finding a leak - cold water pressure test conflicting results in the USA area at PlumbersForums.net

Similar plumbing topics

P
  • Locked
Looking for some help here - not my boiler, so consider me a proxy. I'm also by no means a heating engineer: I'm just looking for pointers, as the...
Replies
3
Views
718
I'll pop this into the general advice forum as it seems the most active, but mods - feel free to move if there's somewhere more appropriate. Thank...
Replies
18
Views
2K
Hi all, I am wondering if someone can make sense of this. I have been trying to determine if there is a leak on an existing water supply pipe...
Replies
6
Views
1K
I have moved plumbing pipes for Ariston lux water heater As far as I can tell have moved and installed all pipe work correctly Fitted expansion...
Replies
0
Views
2K
Hi we had a new boiler fitted about 6 months ago and over the past 2 weeks the boiler pressure has dropped to 0 at least 4 times. It only seems to...
Replies
10
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock