Messages
58
Guys help needed..... greenstar 28i junior...... I can hear it spark but burners don’t come on, then goes to ignition lockout....inlet pressure 22mbar it does not move at all when it’s sparking... gas valve resistance 390 ohms top solenoid 190 ohms bottom.
In sparking voltage to gas valve 10vdc top and 15vdc bottom...... changed gas valve same issue, changed pcb same issue...... albeit second hand valve and pcb...... but the fault is the same 😡😡😡
 
Turn the gas off does the pressure drop on p1 ?
If not need to check if it’s getting the correct signals and power

if it is gas valve

if not pcb
 
Turn the gas off does the pressure drop on p1 ?
If not need to check if it’s getting the correct signals and power

if it is gas valve

if not pcb
Turn the gas off does the pressure drop on p1 ?
If not need to check if it’s getting the correct signals and power

if it is gas valve

if not pcb
no drop in pressure... the trouble is resistance on GV are correct but the voltage when sparking are 10 and 15vdc..... when the manual state 20-30vdc......replaced the pcb with a second hand one same issue, suspect the wiring loom now although it looks ok on visual inspection
 
no drop in pressure... the trouble is resistance on GV are correct but the voltage when sparking are 10 and 15vdc... when the manual state 20-30vdc....replaced the pcb with a second hand one same issue, suspect the wiring loom now although it looks ok on visual inspection

End to end test it would be my next port then on the phone to Worcester to check my voltages if you don’t have the card
 

Reply to Greenstar junior 28i in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hoping someone can give me advice with this one. At an annual gas service today I found a Worcester Greenstar Junior 28i to be using only running...
Replies
10
Views
2K
I need some help with a Worcester Junior 28i gas boiler and I'm hoping someone here may have came across this fault before ... I have checked...
Replies
1
Views
1K
Hi experts, i'm looking for some advice to get to the bottom of my boiler problem. The boiler is a Glowworm Ultimate 40FF so a traditional NOT...
Replies
5
Views
1K
Hello My trusty Vaillant 242 EH is having some issues. It has developed an issue when firing up the burner. The fault is seen with the hot water...
Replies
1
Views
576
In our Village Hall we have a Ideal Concord CXS/SD40/H central heating boiler. This was installed new when we had an extension built and the...
Replies
10
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock