Hi can I start by saying a big thank you to gasman and croppie for there assistance in getting into this forum.

i'M new to the boiler break down gig so please go easy..

I was called out to a Halstead ace 30kw Combi.
problem is no hot water or heating.

on a heating demand boiler only stays alight for 2-3 seconds then flame goes out.
So when there's a call for heat whether that be hot water or heating. Fan and pump engage APS then proves there ignition electrodes spark gas valve opens we have a flame but it only lasts for few second then goes out.

Changed the the flame sensing electrode. Made no difference. Spoke to a mate who suggested pcb. Customer is on a budget so we ended up getting the PCB reconditioned. The guys put old board on a jig that symulated the boiler sequence and all was ok.

Good for the board but I'm now back to square one. Also tested coninuity across the flame electrode leads. All ok.


Anyone have any suggestions where to look next.

Bit more info.

carried out standard electrical tests. Resistance to earth, polarity and Earth leakage all ok




Sent from my iPhone
 
Last edited:
you checked the high limit and ntc probes?
 
you checked the high limit and ntc probes?

Hey Shaun, thanks for the interests.

As I said I'm fairly new to this diagnostics lark but learning fast. I was under the impression I could iliminate that these where at fault given the fan and pump run and the gas valve solenoid opens to fire the boiler and we ge a flame. If these where at fault the the boiler would not fire?
I did check them Anyway and got about 14k ohms on the ntc, high limit stat not checked not sure there is one but there is an over heat stat is this the same thing? But if these where faulty would the boiler still fire?
 
Last edited:
Has there been any electrical work done in the property lately, reverse polarity can cause this
 
Are you sure that the pump is moving anything ? just because it makes a noise doesn't mean its working, be careful if you call Glen Dimplex charge at 60p pr min.
 
Are you sure that the pump is moving anything ? just because it makes a noise doesn't mean its working, be careful if you call Glen Dimplex charge at 60p pr min.

Hey JTS, no did not actually check the pump. just felt to see if was vibrating. but is 2-3 seconds of flame enough to activate the high limit thermister to trigger the boiler to shut down? I checked the continuity on the pump and ohms reading were within range. How do you suggest i go about checking the pump?
 
you checked the high limit and ntc probes?

Hey Shaun, thanks for this.

I checked all the thermisters. But checked them in situe. ie disconnected the leads and tested with multimeter on ohms while cold. Was getting a reading of 14kohms. Should i take them out and test to see if as NTCs ohms reading is decreasing as they warm up?
Also my understanding is if they were faulty this should interrupt the ignition sequence as PCB should confirm this prior to energising the gas valve and spark electrode.
As i stated i'm new to this... just lucky the customer is a next door neighbour he knows i'm fresh but is happy to let me learn on the job as i'm not really charging him much for my time. Just want to make sure i stay safe get it right for him. He's a bit tight for cash...
 
Are you sure that the pump is moving anything ? just because it makes a noise doesn't mean its working, be careful if you call Glen Dimplex charge at 60p pr min.

Hey JTS happy to call Glen Dimplex. Do they do technical for Halstead?
 
Hey Shaun, thanks for this.

I checked all the thermisters. But checked them in situe. ie disconnected the leads and tested with multimeter on ohms while cold. Was getting a reading of 14kohms. Should i take them out and test to see if as NTCs ohms reading is decreasing as they warm up?
Also my understanding is if they were faulty this should interrupt the ignition sequence as PCB should confirm this prior to energising the gas valve and spark electrode.
As i stated i'm new to this... just lucky the customer is a next door neighbour he knows i'm fresh but is happy to let me learn on the job as i'm not really charging him much for my time. Just want to make sure i stay safe get it right for him. He's a bit tight for cash...

it should say in the manual for what temp (water) Resistance is given and no normally they just give a low reading,

and could be giving a 79 degree reading and cutting out at 80 so would only come on for a few seconds

and is pump turning / strong enough

take the center screw out and put a old flat headed screw driver (must be old as could damage the screwdriver ) and put a med to firm push pressure into the pump if you can stop it the pump is gone and a new one is needed

but tbh depending on age of boiler, i would try and get them to replace it (not a very good boiler) as no guarantee on how long it would last after the repair and sinking good money to a bad/ not worth repair
 
don't call halestead dimplex .last time I did it was £5 a min
 
QUOTE=Gas74;878850]Is this the condensing model?[/QUOTE]

no its the condensing model.
But think I'm close to figuring out thanks to you guys.
Think it's either the pump or the flow switch.
Found the halstead manual http://www.freeboilermanuals.com/assets/pdf/halstead/AceHE_installation.pdf
Reading the ignition fault flow chart. Looks like it's the flow switch or pump as the green led is blinking. (sorry if i did not mention this initially) or the pump not triggering the flow switch. I assumed that the boiler would go to lock out and not light if these were faulty. But given it has i'm guess that it's not quite as sequential as this. And the lack of flow/movement is causing the gas valve to shut up shop??? Guessing i can test for voltage at the flow switch pin on the board to see if it's going from NO to NC once the pump has started working? can i also link out the flow switch to see if we flame stays on?
 
Re your question Yes Glen-Dimplex now own Halsted, along with most cookers & fires, total rip-off if you need tec advise, if you have to call them use customers phone. Still think you have a pump problem or blockage.
 
A lot of parts for Halsteads are now obsolete, I have a customer with a pin holed plate hex and it needs a few other bits too, some are obsolete and others are a joke...£47 for an AAV!
 
A lot of parts for Halsteads are now obsolete, I have a customer with a pin holed plate hex and it needs a few other bits too, some are obsolete and others are a joke...£47 for an AAV!

Yes Halsted parts , like calls to Dimplex are expensive !
 
Re your question Yes Glen-Dimplex now own Halsted, along with most cookers & fires, total rip-off if you need tec advise, if you have to call them use customers phone. Still think you have a pump problem or blockage.
jts you are the man!

Ended up being the pump. Start capacitor was knackered. Got one from maplins. Was a little large for the pump head housing but just cut a little of the housing out so it poked through the top and then connected the two flexes with connector blocks . Boilers fires like a dream.

Many thanks to everyone that contributed to helping me get there. Steep leaning curve but with your help slowly getting the hang of things
 
Status
Not open for further replies.

Reply to Halstead ace 30kw gurus please help!! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock