I have an older style open vented heating system with a Glow worm 50/60 RF flued fan boiler. I have a hot water tank on the first floor and two header tanks in the loft, one large for the hot water and a smaller one for the heating.
Last week I removed a radiator from the landing and capped off the pipes under the floor. Since doing this when the boiler switches off there is a loud bang and the whole heating system shakes. I thought it was an air lock but I have bled the system and all radiators are warm. It only does it when it's on heating, not when on hot water. Another point, when the boiler switches off water runs into the header tank for about 3 seconds.p from the expansion pipe.
I've even tried connecting the pipes I cut off together just in case I had messed up the flow and return but it's still the same. All radiators have trv's apart from a heated towel rail in the bathroom and large radiator in the hall which is by the thermostat.
Anybody have an ideas what it might be. I have also flushed the system and it is clean. It's worked fine for years until I removed the radiator.
Many thanks.
Paul.
Do you have an automatic bypass on the system. You may need it if the radiator you removed acted as manual bypass.
It sounds like a spring return motorised valve slamming shut.
Vee may well be right with the bypass but you need to identify the cause first.
If you have a motorised valve, check it when you turn the heating off to see if it’s that, which is making the bang.
If not let us know and we’ll think of something else
It may not have one. I was going off the description you gave. Difficult on a forum.
Normally, airing cupboard or near Boiler !
If it hasn’t got one, maybe an auto bypass is the answer.
Any chance of photos of Boiler and airing cupboard ?
It has two motorised valves. I can hear the motors opening and closing when both the heating and hot water are in use. The bang is really hard to identify, it seems to be coming from around the pump but difficult to say for sure. Is the hot water being pushed up into the header tank part of the same problem.
When I removed the radiator I capped the ends and have also tried connecting them together similar to how the radiator would function but no joy.
Thanks for your advice.
Paul.
Paul.
Paul.
Honeywell ( silver box top ).?
The boiler is in the garage 15 meters from the airing cupboard. Since this problem the bleed valve no longer works and is full of water. If you undo the screw water overflows from the nipple.
Cheers.
Yes it needs a bypass.
If you try holding the valve open whils someone turns heating off you’ll see if it stops the bang
Cheers.
The
How would you do that, I'm not sure. Presume you would take the cover off but then what?
Many thanks.
No. 230V in box.
There’s a lever on side where wire exits.
Auto - Manual
Opposite side to the label on the zone valve is a little lever. When your heating is on there should be no resistance on the lever and it should move left and right freely. Heating off and you should feel tension on the lever and when you move it is should move back to close position on a spring action. Switch your heating off and hold the lever open. If there's no bang once the pump has shut off then you def need a auto bypass. There is also a little nib on the valve where you can hook the lever onto so it won't return to close, if you are doing this alone.
I'll try it in the morning and be in touch then (kids asleep). Thanks for your help and advice, much appreciated. Regards. Paul.
No worries, do let us know how you go on!
Hi I did what you said. When the heating is off I checked the tension on the lever and there isn't any. When it's on there is tension so I held the lever open and turned the heating off and it still bangs.
Could it be an air lock.?
Cheers.
When the heating is on, there shoul be no tension as the valve is open. If it is calling for heat that is.
i.e. programmer on, room stat up above room temp.
Maybe you meant that ?
If it still bangs with the valve left open, it needs looking at, I can’t guess without witnessing it.
I don’t think it’s an air lock but that is my opinion.
Sorry was checking the wrong one. You are right, no resistance when on. I held it open, turned off and no bang. Can still hear water going into header tank? Does this mean the valve is faulty.
Cheers
Cheers
It can be a faulty valve yes but in your case I would suspect that the lack of a system bypass is causing the valve to slam shut as the pressure increases on closing. (valve damage may have occurred as a result of not having a bypass).
My advice:-
Install a system bypass (22mm Auto) and see if it stops the bang. If not replace the valve. You need the bypass anyway.
Agree with the above but as your draining down I would replace the valves at the same time, if you can afford the slightly extra cost
Great help guys thanks very much. One more question where should I fit the bypass valve. Close to the boiler or in the airing cupboard.
Cheers.
They were hissing air when the system was refilling so guess they are air vents.
Airing cupboard
I would fit it in between the port valve tees and straight onto the return
Airing cupboard
Wouldn’t the rad in the hall and heated towel rail act as a bypass. Neither of these have trv’s.
So removing that landing rad shouldn’t have made a difference. He also joined the pipes from the rad he removed and it was still banging.
If these are piped in before any port valves yes they would
Not if they’re after the valve and they most likely are.
The bypass needs to be before the valve for when the valve shuts!
Hi
I had a plumber attend yesterday and the valve was faulty, when taken off you could hear it making a grinding noise. He replaced the valve and the banging stopped but did say it probably needs a bypass valve fitting between the pump and valves then into the return. After a few hours the banging returned but it was much quieter. The plumber said the new valve is much stronger than the old one.
The bypass is being fitted Thursday so I will let you know what happens.
Cheers for all your advice.
Regards.
Paul.
Hi Paul
I would suggest that you check that the zone valves are actually positioned correctly for the differential pressure being created by the pump. The type of sound you have described indicates to me that a zone valve is slamming back when closing - this happens when a valve is positioned the wrong way to the flow - but looking at the photo they seem good to me but obviously I cant see the whole system layout design - so its difficult to be sure whats going on?
Best of luck getting it sorted... Bill
Hi All,
I had the bypass fitted but there is still a slight bang when turning off. It still pushes water into the header tank as well. I also had fitted a new pump as the old one was nearly blocked. I have fitted a magnaclean on the return to the boiler and you wouldn't believe what muck came out of it in 24 hours.
Should I just put the radiator back.
Cheers.
I would drain down and wack some x800 in the system for a week then drain it down again and fresh inhb
I already did flush and the water ran clean. I opened all the bleed valves to get all the water out. The pump was old, dated year 2000 so it needed replacing anyway.
Just updating again on this. I refitted the radiator and now the heating Bangs even more. Really am at a loss. Anybody with any further ideas.
The fact that you have water flowing out the vent pipe when the system shuts down indicates you still have a fault, probably a blockage somewhere near the expansion pipe. You could try turning the speed on the pump down to its minimum to see if the noise reduces. Another thing to try would be to remove the rad again, empty it, refit, turn on the valves but don't bleed it. (it should act as an expansion vessel).
One thing i noticed looking at the pictures is the vent from the boiler looks like its running horizontal along the ceiling, so it may be possible that the system has an air lock.
Forgot to say, that as you mentioned the amount of muck in the magnet suggests that the system needs a good clean.
Thanks for your advice. The pipe or pipes running across the garage ceiling are the flow and return to the boiler. The vent pipe is in the airing cupboard and goes about 18 inches abouve the header tank in the loft. When filling the heating back up after draining it doesn't bang, it's only when all the air is out the system so similar to your radiator test. Turning the pump down reduced the bang noise.
Cheers.
Paul.
Got a picture of the new by-pass that’s been fitted ? Hard to tell from airing cupboard picture but is the open vent an cold feed teeing in just before pump
Where's the bypass valve all I see is a full bore ISO valve ?
The valve put in on the by-pass looks like a ball fix turned 1/3 off have you tried opening this fully an seeing if this stops the banging
*shaun beat me to it,but that isn’t correct for a by-pass that’s why you still have the banging
The plumber said it didn't need one, I thought it might and I asked again whether it needed to be 22mm. I can change it myself if you are able to advise what to get and where to put it. If the valve is fully open then yes it does stop it banging.
One question, I have lived in the house for 13 years without a single bang. Why would this start after removing the radiator.
I didn’t even pick up on that it was 15mm,that won’t help an then with the type of valve that will neither. You’ve said that with it fully open the banging stops.I could only say that since the 13years you’ve been there that the pipework /heatexchanger has become restricted.
Cheers for your help. Could you tell me what valve I need and where it should go.
I assume the valve is operated by bar pressure
Reply to Heating Bangs when switching off. in the Plumbing Jobs | The Job-board area at PlumbersForums.net
PSxxxxxx