Discuss Hep2o in plastic conduit in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Messages
122
I want to bury some 25mm plastic conduit in the wall to allow me to run the flow and return between the downstairs and upstairs, obviously it would mean the pipe is unsupported through the length about 2m. It will be supported top and bottom. Would this be okay.
 
Probably fine on copper or plastic plumbing pipes.
I have run 15mm copper pipes inside 20mm electric conduit on jobs.
 
Sorry, I wondered had I imagined that Hep was mentioned, then I see it was in the title of the thread. :)
Hep inside plastic conduit will be no different than the pipe in pipe Hep really, so should be fine.
 
Make sure the hep pipe is a slack fit inside the conduit.
You need to have the heating pipes with a bit of space around them as risk of noise as they heat and cool and expand & contract.
 
I want to bury some 25mm plastic conduit in the wall to allow me to run the flow and return between the downstairs and upstairs, obviously it would mean the pipe is unsupported through the length about 2m. It will be supported top and bottom. Would this be okay.
What type of wall are they going into?
 
as long as you plaster them in it will be fine
 
Be chased into the brick work and plastered over. I will probably put three lots of the 25mm in, never know what I might need to run in the future.
I would still prefer to use protected copper or barrier pipe.
 
Ohhhhh. Ok. For some reason I thought that it was normal plastic?. Sorry my bad.:oops::oops:
 
Status
Not open for further replies.

Reply to Hep2o in plastic conduit in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have about 6 metres of 22mm PEX to run through concrete and understand I need to have it in flexible conduit to offer a bit of protection and...
Replies
3
Views
665
Hi all. Shower is leaking into downstairs when water is being aimed at wall . All sealant has been redone on outside and between shower tray and...
Replies
4
Views
321
I am trying to workout in what order my radiators heat up in order to then balance them. I am able to figure out which radiator pipe is the...
Replies
1
Views
345
Evening all. Not sure if this is the most appropriate place to post this in the forum, happy to move if not. I'm looking for a metallic 32mm...
Replies
7
Views
655
Hi all, Have got an old 60/70s PVC soil stack, the Toilet is going into a Hunter branded socket which has an old O-ring design (quite flat with 3...
Replies
2
Views
549
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock