my girlfriend just moved into a new house and today i was removing the fire, and when i done my usual checks i thought I'd check the inlet pressure as the Boiler kept on cutting off, think it was the pilot light going out. The Pressure at the Meter is 25mbar, is this 2 high?
 
standing. i just checked it after my tightness test with no appliances on.
 
i went to one today and the standing pressure at the meter was 58mbar, turned it off and connected the gas supplier
 
A low pressure gas supply can have the pressure at the ecv up to 75mb although it is normally in the 30's.
The regulators are designed to lock up at a pressure not exceeding 30mb so a standing pressure at the outlet of up to 30mb is acceptable.
A standing pressure test proves nothing other than the regulator is locking up within limits and you have gas.
When the gas flows through the regulator the working pressure should be within the range 23 to 19mb (21+or-2). At low flow rates it will tend to be nearer 23mb.

The one diesel was at today with a standing pressure of 58mb had a faulty regulator which was failing to lock up.
 
In some areas I have seen the standing pressure being a consistent 25-26 mbar.
Nothing to worry about, as long as your appliance input and operating pressures are not too high which would mean a call to the service provider to have the regulator pressure turned down slightly.
 
standing pressure is a strange cookie,

as the design of these reg's used is really only limiting overpressurising the system i suppose upon the cease of gas flow. Ultimately the regulator is a mechanical moving part, and can only react so fast. So with as said 70 odd millibar behind it on the trannys side, its no supprise the odd mbar gets through when gas stops flowing. Obviously the higher it is, the more problems will be caused. 21 +-2 is the most important figure i have ever lodged in my head i think.
 
Depends where you live. Low pressure mains are normaly maxium 75mbar. High usage area's may vary. The supplier shouls provide 21mbars at the meter but are only legally required to provide 12mbars. total nonsense when appilances generaly require 20mbars on the inlet.
 
In some areas I have seen the standing pressure being a consistent 25-26 mbar.
Nothing to worry about, as long as your appliance input and operating pressures are not too high which would mean a call to the service provider to have the regulator pressure turned down slightly.

Can the regulator not be adjusted by RGI ? always adjusted regulators myself if they are not faulty
 
Status
Not open for further replies.

Reply to high inlet pressure at meter in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock